默认 minimum concrete cover tolerance

minimum concrete cover tolerance
per aci 381-05, section 7.5.2.1, the tolerance on minimum cover reads -3/8" for d<=8" and -1/2" for d>8". for tilt-up wall panels, the delegated engineer on my project has specified a minimum clear cover of 3/4". we have found locations where the reinforcing is very close (<=1/2") to the face of panel, with even some locations the rebar showing.
the way i am reading this tolerance is subtract the tolerance value from the minimum clear cover. so for 3/4" minimum clear and a d<=8", this would allow the minimum clear cover to be as small as 3/8". this to me seems unreasonably close. shouldn't these tolerances be (+) instead of (-)???
nick deal, p.e.
michael brady inc.
i'm sure you are meaning aci 318-05. you must also read the text, not just the table, where the text provides a tolerance for "cover shall not exceed minus 1/3 the minimum concrete cover required in the design drawings and specifications." reiterated in aci 117 where "reduction in cover shall not exceed 1/3 the specified concrete cover." this seems reasonable to me. it seems to me if you are missing cover concrete, you may also have an issue with consolidation.
greg
the tolerances given in 318 are in reference to the design capacity of the member and as such, locate the tension steel such that a reduction in d is minimized, but an increase in d is allowed, such that cover is not compromised. as noted above, an increased d does not relieve the requirement for cover and aci 117 provides a more in depth review of the requirements.
the tolerance for d and the tolerance on allowable clear cover are seperate items. in typical construction, they are at adds, but both must be satisfied.
it appears in your case, the cover tolerances have been violated in construction and a means of remediation must be determined.
with 3/4" minimum cover, reducing that by 1/3 would give a minimum allowable cover of 1/2". if you are able to see bars at the surface and tell that bars are 1/2" below the surface, you have additional issues as noted by greg.
the revised 117-06 does a pretty good job of giving more detailed explanations of tolerances noted. take a look.
daniel toon
__________________
借用达朗贝尔的名言:前进吧,你会得到信心!
[url="http://www.dimcax.com"]几何尺寸与公差标准[/url]
huangyhg离线中   回复时引用此帖
GDT自动化论坛(仅游客可见)
回复


主题工具 搜索本主题
搜索本主题:

高级搜索
显示模式

发帖规则
不可以发表新主题
不可以回复主题
不可以上传附件
不可以编辑您的帖子

vB 代码开启
[IMG]代码开启
HTML代码关闭

相似的主题
主题 主题发起者 论坛 回复 最后发表
concrete sampling guidlines huangyhg 产品功能分析 0 2009-09-08 12:34 PM
concrete mix= reinfocing for exterior composit deck huangyhg 产品功能分析 0 2009-09-08 12:19 PM
concrete corrosion in partial saturated condition huangyhg 产品功能分析 0 2009-09-08 11:54 AM
chapter 4 preliminary design properties of concrete huangyhg 产品功能分析 0 2009-09-07 11:23 PM


所有的时间均为北京时间。 现在的时间是 10:17 PM.


于2004年创办,几何尺寸与公差论坛"致力于产品几何量公差标准GD&T | GPS研究/CAD设计/CAM加工/CMM测量"。免责声明:论坛严禁发布色情反动言论及有关违反国家法律法规内容!情节严重者提供其IP,并配合相关部门进行严厉查处,若內容有涉及侵权,请立即联系我们QQ:44671734。注:此论坛须管理员验证方可发帖。
沪ICP备06057009号-2
更多