默认 mud slab over top of drilled pier

mud slab over top of drilled pier
i am working on a project where concrete walls will span between drilled piers. will not have grade beams, maybe just a mud slab to set wall forms on. there are fairly heavily loaded pilasters at the piers, supporting concrete columns above. contractor says for this condition they like to hold the pier down a few inches and run the mud slab over the top of the pier, in order to have a more finished surface to set the forms on, since top of drilled piers are typically very rough. has anyone seen this done before and/or have any precautions?
are the walls precast? if so you will have eccentric loads on the piers when there is wall on only 1 side.
also check that the corner is not going to break off.
csd
so are your column and wall connections interupted by the mud slab if you run the slab over the top of the pier? can the mud slab transfer the forces from the
walls are c.i.p. the mud slab would need to have strength adequate to transfer compression from pilaster to pier.
sounds like you have a thinking contractor. there is nothing wrong with his approach as long as the concrete in the "mud slab" will transfer the load from the walls and pilasters to the pier, and the reinforcement laps occur above the "mud slab". need to consider also any lateral loads you have.
is the "mud slab" blinding concrete with a low compressive strength? in this case it cannot usually be used in place of structural concrete.
i assume the "drilled piers" are what i would call bored piles. aren't they constructed using either bentonite or polymer excavation support? if this is the case they need to be cast high and then trimmed to the correct level.
otherwise why not just cast to the correct level and then spend some time getting a good enough surface to set the forms on.
the piers are 4' to 6' diameter.
the contractor is trying to save the cost of extra formwork at the caisson. i would have him stop the mudslab short of the caisson and provide the extra formwork and waler at the bottom across the width of the caisson.
jike, didn't understand that.
is my decription correct. the drilled piers (4' to 6'in diameter)will have cast in-situ walls between them. directly above them the piers will have a rectangular column, which is in effect a thickening of the wall (a pilaster)
the pilaster will need formwork, the contractor intends to cast bliding concrete (mud slab) on which all this formwork will sit.
what we don't know is the dimension of the pilaster compared to the drilled pier. assuming the pilaster is larger than the drilled pier the mud slab can surround the pier but not run over the top of it.
if the pilaster is of smaller dimension than the pier and the forms somehow have to sit on the pier then structural concrete wll have to be used.
the formwork for the walls and pilaster is essentially all part of the same except the pilaster is bumped out on one or both sides. i am assuming that the bottom of the mudslab is even with the top of the caisson then the top of the mud slab is higher and does not extend over it, then there will be a some area below the form that needs to be fill in with more formwork.
the overall footprint of the pilaster (including wall thickness) is 20" x 36", which is smaller than the minimum drilled pier size (48") we will be using.
__________________
借用达朗贝尔的名言:前进吧,你会得到信心!
[url="http://www.dimcax.com"]几何尺寸与公差标准[/url]
huangyhg离线中   回复时引用此帖
GDT自动化论坛(仅游客可见)
 


主题工具 搜索本主题
搜索本主题:

高级搜索
显示模式

发帖规则
不可以发表新主题
不可以回复主题
不可以上传附件
不可以编辑您的帖子

vB 代码开启
[IMG]代码开启
HTML代码关闭

相似的主题
主题 主题发起者 论坛 回复 最后发表
how to thicken an existing concrete slab on grade huangyhg 产品功能分析 0 2009-09-09 05:54 PM
hairline cracks in post tensioned slab huangyhg 产品功能分析 0 2009-09-09 03:43 PM
cracks in two-way flat slab huangyhg 产品功能分析 0 2009-09-08 02:29 PM
crack in old floor slab huangyhg 产品功能分析 0 2009-09-08 02:20 PM
concrete spec. for slab-on-grade huangyhg 产品功能分析 0 2009-09-08 12:49 PM


所有的时间均为北京时间。 现在的时间是 05:43 AM.


于2004年创办,几何尺寸与公差论坛"致力于产品几何量公差标准GD&T | GPS研究/CAD设计/CAM加工/CMM测量"。免责声明:论坛严禁发布色情反动言论及有关违反国家法律法规内容!情节严重者提供其IP,并配合相关部门进行严厉查处,若內容有涉及侵权,请立即联系我们QQ:44671734。注:此论坛须管理员验证方可发帖。
沪ICP备06057009号-2
更多