默认 mwfrs or c=c

mwfrs or c+c
in a typical one story building with a joist girder/joist/steel deck roof system supported by on interior columns and exterior cmu walls, what kind of wind loading do you consider for design of these items??
cmu walls - mwfrs
columns - mwfrs
girders/joists/steel deck - mwfrs or c+c - the roof diaphram as a whole transfers wind loading back to shear walls, therefore are each of these items designed with mwfrs.
my confusion primarily lies with the roof system since to me they act together to transfer wind loading but as seperate items (not working together as a diphram) they would be more under a c+c item? so waht loading(s) would you consider when designing these items?? also what are the thoughts of connection designs of the deck to the joist and the joist to the joist girder and teh joist girder to the walls? i have heard two schools of thoughts on these connections as well and to me it seems that these connections shoudl definitely be designed to resist the c+c loading.
so waht are your thoughts on this subject??
chris
check out our whitepaper library.
you need to design the roof diaphragm and shear walls using the mwfrs loads. for individual elements, like cmu walls, roof girders, roof deck, etc. etc. you need to use the c & c loads. the c & c loads should be higher, since there's more of a chance of a maximum wind load on a smaller area than a whole building.
if it seems like some items are designed in one direction for one load and in the other direction for another load, you're probably doing it right.
i agree with jedclampett, but would also like to add the following: the c&c loads are higher for more of a reason than just the smaller area. c&c loads are also greatly affected by the location on the building - the end zones on the roof and walls see much larger loads.
jed is also right about designing each item for possibly both mwfrs and c&c - the most obvious is the cmu walls. i would design the shear wall loads with mwfrs and the out-of-plane loads as c&c.
first let me say thank you for all your help so far, i really appreciate it. second, let me clarify this:
1. shear walls (cmu walls for my individual case) - mwfrs wind on wall perpendicular to wind and transfer the shear loadings (thru roof diapham) to the walls parallel to the wind (shear walls).
2.cmu walls - (c+c) design individual walls perpendicular to wind load (for bending moment) with the appropriate c+c wind pressure.
*** summary for cmu exterior walls (shear - mwfrs) & (moment - c+c)
3. roof system - joists / joist girders / deck - (c+c) +/- pressures.
****the positive pressure by the wind are rarely controls any design for downward (bending of joists/j girder) in my area of the country.
*** the(c+c) uplift wind forces are provided on the drawings for the joist manufacturers so that they can design their joist and joist girders to resist the uplift pressure.
question: do joist manufacturers design their joists and joist girders to resist the full uplift (c+c) pressures generally or do they reduce it by a fraction of the dl allowed by asce 7?? just curious??
4. roof diapham - mwfs - all connections transfering loading to shear walls (such as the puddle welds between the deck and joists since these cause the roof system to act as a diaphram). am i forgetting any other crucial connections that should be designed under mwfrs wind pressures?
thanks again for your help.
chris k
to answer some of your questiona:
it sounds like you you have the right idea.
some critical design aspects that ae commonly missed are the attachment of the ledger angle to the cmu wall to transfer mwfrs loads. there's also a minimum value in the code.
i'm not sure what reductions in uplift you're referencing, but as far as what the joist people design to, it is kind of up to you. you can tell them no reductions. or better yet, give them a diagram of the downward and uplift forces. it's very common. another trick you can use is to assign a dead load for uplift only, less than the one for the downward cases. when you calculate your dead loads, you're probably conservative with their values. but for uplift, you want to be conservative in assuming that there's nothing there except your roof deck.
for uplift on joists and joist girders, we create a diagram called "net uplift". we calculate this from the equation 0.6d - w to get the "net" uplift.
i hope this helps!
i've put net uplift for joist design on the plans before and calculated it using the dead load i wanted and the load combination 0.6d+w.
it's a little easier in my mind for cmu wall design to think of it as mw for in-plane forces and c&c for out-of-plane forces. joists and trusses are part of the c&c unless they are being used to transfer part of the mw forces, which would call for a separate load case. an example of this would be a joist used for a drag strut. again, that would still be mw for in-plane forces and c&c for out.
keep in mind that if your effective or actual tributary area exceeds 700 ft2, you can use mw regardless. asce 7 6.5.12.1.3.
a metal deck diaphragm is another one where the mwfrs is used for lateral load transfer to vertical wind bracing and c&c loads for uplift and fastener design.
also when using c&c loads make sure to use the right trib area, so that the loads are not larger than they need to be. for masonry walls i usually use l^2/3 which is allowed in asce 7 because masonry walls are typically designed on a per foot basis. this rule would apply to joists as well if the trib area is less than l^2/3 use l^2/3 instead.
good point ash. also, in the same manner, you can use span/3 for the width of wall studs. this will reduce the wind load significantly.
thanks everyone for your insight. i really appreciate it.
you have all cleared up alot of issues for me.
chris
__________________
借用达朗贝尔的名言:前进吧,你会得到信心!
[url="http://www.dimcax.com"]几何尺寸与公差标准[/url]
huangyhg离线中   回复时引用此帖
GDT自动化论坛(仅游客可见)
 


主题工具 搜索本主题
搜索本主题:

高级搜索
显示模式

发帖规则
不可以发表新主题
不可以回复主题
不可以上传附件
不可以编辑您的帖子

vB 代码开启
[IMG]代码开启
HTML代码关闭

相似的主题
主题 主题发起者 论坛 回复 最后发表
mansard roof and mwfrs huangyhg 产品功能分析 0 2009-09-10 12:16 PM
hvac screen - mwfrs or cc huangyhg 产品功能分析 0 2009-09-09 06:15 PM
consider it as mwfrs or cc huangyhg 产品功能分析 0 2009-09-08 01:21 PM
cmu wall design cc load combo questions huangyhg 产品功能分析 0 2009-09-08 09:39 AM
cc or mwfrs huangyhg 产品功能分析 0 2009-09-07 11:12 PM


所有的时间均为北京时间。 现在的时间是 05:54 PM.


于2004年创办,几何尺寸与公差论坛"致力于产品几何量公差标准GD&T | GPS研究/CAD设计/CAM加工/CMM测量"。免责声明:论坛严禁发布色情反动言论及有关违反国家法律法规内容!情节严重者提供其IP,并配合相关部门进行严厉查处,若內容有涉及侵权,请立即联系我们QQ:44671734。注:此论坛须管理员验证方可发帖。
沪ICP备06057009号-2
更多