reinforce existing steel beam for deflection
i have a 3 span continuous steel beam, uniform load on top flange. contractor wants to remvoe the two interior beams. beam has adequate strength without the two interior columns, but fails the deflection criteria. does anyone know of any references or articles that discusses how to calculate the amount of reinforcing needed to reduce the beam deflection.
does the reinforcing have to be the full length of the member?
i think i can do a 3 member model with the middle member being the reinforced part. and by changing the middle member properties and moving the two interior nodes out, i can determine the reinforcing required and how long it needs to be. does anyone know of a better mouse trap?

sounds like you are on the right track. i find on this type of problem, trial and error works best. i don't know of any formula that will lead you to the correct answer quickly.
my experience is the amount of reinforcing needed will be more than you expect. for example, don't start with a cover plate on the bottom flange--start with a wt welded to the bottom flange!
daveatkins
this is residential. beam is supporting a loft. loft floor framing is sitting on top of bottom flange, which puts the bottom of bottom flange roughly at ceiling level. can't add much to bottom of bottom flange due to head clearance. maybe a thin hss. or might just have to add angles welded to web and top of bottom flange.
twinnell
you need to drastically increase the beam inertia, and whatever you do, this will require you to make the beam deeper. this thing is going to get real heavy, real quick, if you can't increase the depth.
don't forget to check (and most likely reinforce) the beam's end connections, and maybe the remaining supporting columns.
with all due respect, this is much more than a "moving the nodes" exercise. your reinforcement needs to extend past the nodes in your analysis, in order to develop the strength of the reinforcement. you should discuss this with a more experienced engineer.
tg
i've often wondered about doing this. i wanted to do this to my own house in the basement but don't know how to go about beginning to check the concrete basement walls or footings without knowing what is in the walls or how big the footings are or what the allowable bearing pressure of the soil is.
would you shore the entire basement framing at the beam with makeshift walls while you remove the post(s) and reinforce the beam?
it just seems like much more of a task than simply reinforcing the beam.
can you leave a cantilevered length at the end past the interior column? this will provide you with some continuation and reduce the deflection.
alternatively moment connect to the columns and beef these up as necessary.
i have to apologize. my original post should have said...the contractor wants to remove the two interior columns...not beams. there is only one beam.
there is hardly any load on this beam...beam end reactions after the interior columns are removed is only 5 kips. the problem is that the beam is a w8x35 and is 29 feet long. it is supported at the ends by steel columns..not by walls.
i know how to reinforce steel for strength, never had to do it for just deflection.
i see three options...
1. weld two 8" deep plates to the flanges, one each side of the beam to create a box section, thickness dependent on inertia requirements, and,or
2. add more beams parallel to the existing beam to reduce the tributary width, and, or
3. add another one or two beams transverse to the existing beam with moment connections at the splice points to serve as supports where the columns used to be. this would be two way beam action, with equal deflections at the points of moment connection for load analysis.
mike mccann
mccann engineering
this rolled steel beams can be strengthened with partial-length, adhesive-bonded carbon fiber-reinforced polymer (cfrp) plates. this is the easiest solution to the problem, with no distrubance at all.
zaes73,
will that help with deflection? my hunch is that the steel modulus of elasticity is a lot higher than the cfrp modulus of elasticity, and so the cfrp would not help much with stiffness.
daveatkins
you could still look at making it into a portal frame and beefing up the end columns to take the additional moments.
if this doesnt quite work then combine it with stiffening the beam.
__________________
借用达朗贝尔的名言:前进吧,你会得到信心!
[url="http://www.dimcax.com"]几何尺寸与公差标准[/url]
huangyhg离线中   回复时引用此帖
GDT自动化论坛(仅游客可见)
回复


主题工具 搜索本主题
搜索本主题:

高级搜索
显示模式

发帖规则
不可以发表新主题
不可以回复主题
不可以上传附件
不可以编辑您的帖子

vB 代码开启
[IMG]代码开启
HTML代码关闭

相似的主题
主题 主题发起者 论坛 回复 最后发表
question regarding floor support beam installation huangyhg 产品功能分析 0 2009-09-15 03:58 PM
new to existing concrete beam connection huangyhg 产品功能分析 0 2009-09-10 04:22 PM
lateral support - steel beam huangyhg 产品功能分析 0 2009-09-10 09:52 AM
cantilevered steel i-beam capacity huangyhg 产品功能分析 0 2009-09-07 10:45 PM
12 x 6.5x 38 thick x 41 residential basement i-beam con huangyhg 产品功能分析 0 2009-09-06 10:30 PM


所有的时间均为北京时间。 现在的时间是 02:50 PM.