removing existing building column
i'm evaluating a request from a client to remove the bottom half of an existing column from a building. the bays of the building are 17'-4" currently, and the owner would like one 34'-8" wide bay. the two bays where the column is located are configured as shown.
_____________
| / \ | / \ |
|/____\|/____\|
| | |
| | |
the request is to remove the bottom half of the middle column of the two bay arrangement shown above.
to me, the most logical option is to place a new beam directly under the cut off point of the column to pick up the load from the column. i would like to avoid adding new columns for this beam, but i think this might be inevitable. i would prefer to anchor the beam ends to the existing columns, but i'm still contemplating the feasibility of this. the existing columns are old built-up members of angles and plate. the columns have had concrete added to them over the years and adequate drawings do not exist.
there is a 60 ton crane in the building and the new beam will also have to support the roof loads.
any suggestions or comments on supporting the load from the cut off column?

i've once done a crazy space frame above the roof which spans across the columns that are cut. there were hanger rods at the removed columns to transfer the original column load to the space frame.
space frame itself had to be analysed as well as checking for the existing columns and footings for the space frame reaction.
columns had to be strengthened and footings had to be underpinned and enlarged. very expensive solution but there was no alternative.
the remaining two columns have been encased in concrete?
don't forget to check the foundations.
can the existing upper beam be reinforced to take the new load? by welding additional steel to it?
the remaining columns have concrete around them. without having any existing drawings on the columns/concrete, i can't really classify them as encased in concrete. it appears that heavy plates were riveted to the existing column flanges (for added protection) and concrete was cast between the flanges.
existing foundations are definitely a concern and will be checked if additional load is added to them.
the upper most beams are two simple span runway giders. i would rather leave these alone. the lower beam is truly encased in concrete. however, i don't have any information on the reinforcing around the beam or the size of the steel beam encased in concrete. so i was trying to avoid utilizing that beam.
that's how i arrived at the present idea of using a steel beam header to take the load from the column slated for removal.
can you modify the bracing to transfer the gravity load from the central column to the adjacent columns? i've done something similar before.
|--------|--------|
| \ | / |
| \ | / |
| \ | / |
|--------|--------|
| |
| |
| |
ctw -
the first thing i thought of was that of lateral instability. is this an issue here with a new beam? would the new beam have any type of floor or other lateral stiffening entity? if you cut off the lower half of the middle beam, and the new beam is placed at that level, i doubt there would be any type of lateral constraint and that would be a big issue in my book.
i would second the idea dbuzz presented, using the upper level to form a large story-high truss system. each existing piece of the remaining structure would have to be thoroughly checked and this may mean really closely inspecting the existing beams and columns. the load would of course be dumped to the adjacent columns and footings and i would expect that they are inadequate.
also, with an existing crane - there is also the issue of fatigue to review. and any time you replace a column with a flexural
dbuzz-
nice idea. i'll look into that. this may be a little more difficult to do since the existing columns have concrete around them, but i like the idea.
jae-
the lateral stability was one of the reasons i was seeking some other options for this design. the existing columns and footings will be checked. the building used to have (2) 60 ton cranes in it, but one of the cranes has since been removed. so i expect the existing columns and ftgs to check out ok. fatigue should not be much of an issue in this case. the crane used to see continuous use but it is now only used as a service crane for the main operations.
good point about the deflection immediately after removing the column. this is a good reason to seriously consider dbuzz's idea.
as usual, i agree with jae. i think dbuzz has a good idea, too.
well, "my" idea was to agree with dbuzz....but thanks anyway!
good point though from jae about the increased load on the two "outer" columns and associated footings. the tributary area will be effectively doubled. it's unlikely there is that much "fat" in the original design.
__________________
借用达朗贝尔的名言:前进吧,你会得到信心!
[url="http://www.dimcax.com"]几何尺寸与公差标准[/url]
huangyhg离线中   回复时引用此帖
GDT自动化论坛(仅游客可见)
 


主题工具 搜索本主题
搜索本主题:

高级搜索
显示模式

发帖规则
不可以发表新主题
不可以回复主题
不可以上传附件
不可以编辑您的帖子

vB 代码开启
[IMG]代码开启
HTML代码关闭

相似的主题
主题 主题发起者 论坛 回复 最后发表
out of plumb column huangyhg 产品功能分析 0 2009-09-15 10:59 AM
existing steel column analysis huangyhg 产品功能分析 0 2009-09-09 08:59 AM
coverplating existing columns huangyhg 产品功能分析 0 2009-09-08 02:16 PM
cantilever steel beam at column huangyhg 产品功能分析 0 2009-09-07 10:40 PM
another aci slender column question huangyhg 产品功能分析 0 2009-09-07 12:13 PM


所有的时间均为北京时间。 现在的时间是 03:36 AM.


于2004年创办,几何尺寸与公差论坛"致力于产品几何量公差标准GD&T | GPS研究/CAD设计/CAM加工/CMM测量"。免责声明:论坛严禁发布色情反动言论及有关违反国家法律法规内容!情节严重者提供其IP,并配合相关部门进行严厉查处,若內容有涉及侵权,请立即联系我们QQ:44671734。注:此论坛须管理员验证方可发帖。
沪ICP备06057009号-2
更多