默认 retaining wall - driving moments greater than resisting mome

retaining wall - driving moments greater than resisting mome
i have a retaining wall (floodwall) with water on the left hand side and the soil only about 2 ft above the heel and the toe. so the retaining wall is being driven from left to right. i am making point a at the bottom of the toe (which is on the right side). due to the loads and limited construction space i plan to put this retaining wall on piles.
when i calculate the driving moment (water, at rest pressures, and uplift) and resisting moment (weight of water above heel, weight of concrete, weight of soil and passive pressure)about point a (bottom of toe) the driving moments are greater than the resisting moment. so when i sum the moments i obtained a moment in the clockwise direction.
when i try to figuere out the location of the vertical resultant (pointing up), the resultant has to be to the right of point a (not within footing), for the sum of the moments to be equal to zero.
i guess typically, the resisting moments are greater than the driving moments so you have a counterclose-wise moment at point a, resulting in the vertical resulant point up, and to the left of point a (within footing).
does it make sense to have the vertical resultant to the right of point a (not within footing) because of the driving moments are greater than the resisting moments? or is this something that is not appropriate and need to consider another proccess?
thanks, really appreciate your comments.
hi!!
looks more like a dam for me.
why not try dam & earth retaining fora here.
otherwise i would simply try to change the dimentions so i would not have such a big diference in the moments.
for a dams if i am not mistaken(please corct me team)you should never get an uplifting at the back of the foundation.
the other thing to take into account is the type of the soil. make sure the water do not pas underneath your wall.
y
you will definitely need to consider flow under the wall for this condition.
i recommend that you check out the corps of engineers engineering manual (online) to get some idea of what your doing....sounds like a beginning effort.
regards,
qshake
eng-tips forums:real solutions for real problems really quick.
the resultant cannot be to the right of point a. this would mean the structure is unstable.
daveatkins
gman,
shouldn't your piles be providing uplift resistance? this could be your problem. note that uplift is not usually included in overturning calculations as an external force. usually any buoyancy issues are addressed by modifying the submerged unit weight of the materials.
jeff
jeffrey t. donville, pe
ttl associates, inc.
due to my construction space of less than 20 ft i cannot construct a levee. intially i was designing a floodwall (approximately 16 ft) but i was not able to fit my footing within about 20 ft of right of way. i was not able to meet the sliding safety factor due to the water pressures. yes, geotech is looking at seepage under the wall. at this point i am not really sure if the piles should be providing uplift resistance.
appreciate your advice and any suggestions on what i should might consider doing.
thanks

you don't say how tall the floodwall is, so its hard to give a judgement or check this, but if your net moment is overturning, as you describe, then your structure is unstable. end of story. check loads and/or redesign.
you should have a net restoring moment and the issue should be whether or not the resultant is in the middle third of the base, or whatever criteria you feel comfortable with.
i have to design the wall about 16 feet high, which support pressures due to water. my initial intent was to make this a fooldwall, but the footing was too long for my construction area.
so now i looking into designing a pile supported retaining wall. i am using the methodoly by foundation engineering: peck, hanson and thorburn.
i have increased my footing width to make the resisting moments (173 k-ft) greater than the overturning moments (165 k-ft). i know this is just by 8 k-ft. also by doing this the resultant is within the footing area - but just barely.
should my intent still be to place the resultant within the middle 1/3 even if i am using piles? appreciate all your help and advice.
thanks
i would suggest using a helical pile to "tie down" the footing. this type system will provide anchorage and give you the ability to resist the moments and driving forces needed to keep your footing within the limits of the right-of-way. helicals can be placed wherever you require a resisting force on your moment arm. typically, you can produce 30 - 50 kips of force (depending on soil types) with each helical screw. i have used anchors on cantilevered walls on 10' spacings to resist the uplift pressures discussed in the corps of engineers flood wall manual to help decrease the footing lengths.
if your resultant is "just barely" within the footing, then chances are you are exceeding the allowable bearing pressure in the soil. when your resultant force is not within the kern limit, then the bearing pressure at the toe of the footing is equal to (2*p)/(3*a*b), where p is the magnitude of the resultant force, a is the distance from the resultant force to the toe of the footing, and b is the width of the footing (usually 1', since we design a 1' strip).
daveatkins
another option is to retain the balance of the slope and use a reinforced structure of soils that allows the exchanges of low flow during high flood and has thus to be of adequate permeable state to take the flow without stress in the structure through fine materials causing a surge effect and of course any erosion at weak points. this is not assisted by subsidence zones.
loadings then have to be taken as for a semi-saturated soil as the terminology goes and of course some seepage tolerated at the rear wall site
or of course just raise and bed the sediments above this but this adds to the surge toward the flood.
regrading always leads to some settlement which you will have been trying to avoid according to your description and i concur with the instability comments made by others replying.
the only answer with mathematics is to stay with the formulae and precepts for design and if it does not work out then think of something else and tell the client so.
client demands may try options and i have programmes that will provide hundreds as i was tired of people producing one answer because the data did not exist, the data had to be assessed every time and calculations took so long. this leads to risks and stops students forming one design and going for coffee for the rest of life
but they do need a careful ce approach and knowledge of your expected end result, which you do have clearly.
the answer is much the same, try options of moving the wall, changing the configuration, or possible trench in the base and re-design of the foundation, but as we all know if the big river scours out the basal sediments we are all in it, something politicians fail to appreciate
mike stagg
__________________
借用达朗贝尔的名言:前进吧,你会得到信心!
[url="http://www.dimcax.com"]几何尺寸与公差标准[/url]
huangyhg离线中   回复时引用此帖
GDT自动化论坛(仅游客可见)
 


主题工具 搜索本主题
搜索本主题:

高级搜索
显示模式

发帖规则
不可以发表新主题
不可以回复主题
不可以上传附件
不可以编辑您的帖子

vB 代码开启
[IMG]代码开启
HTML代码关闭

相似的主题
主题 主题发起者 论坛 回复 最后发表
moment transfer at base of retaining wall huangyhg 产品功能分析 0 2009-09-10 03:02 PM
in enercalc masonry wall design, what is parapet heigh huangyhg 产品功能分析 0 2009-09-09 07:17 PM
foundation wall 40 feet below grade huangyhg 产品功能分析 0 2009-09-09 01:38 PM
cantilever retaining wall or no huangyhg 产品功能分析 0 2009-09-07 10:39 PM
buttress wall relative rigidity huangyhg 产品功能分析 0 2009-09-07 05:57 PM