shear resistance with standard base plate
when a base plate sees more shear than available friction, what actually happens? certaintly the anchors go into bending. after some deformation would it not be reasonable that a concrete wedge forms as shown in the following sketch? wouldn't that in turn add to the friction available?
does anyone know of research or designs based on something like this?
on my current project, i have i have the following;
rxns;
.6d+.7e 97k uplift & 57k shear
d+l+.7e 337k down & 57k shear
w12x79 column.
so, i need to pretension the anchor rods in order to overcome the 97k uplift. aisc doesn't recommend that either... wouldn't that be pretty simple though?
wouldn't pretensioning them reduce the capacity of the concrete breakout cone? well, i guess it wouldn't reduce the capacity of the cone, but it would reduce the load that could be place on the anchors from the column before the concrete would fail (from tension on the anchor rods).
hi,
i have a report in german exactly about that problem.
there are 2 possible states of equilibrium for uplift:
1. if the anchors are not pretensed an long enough, the anchors bow in the direction of the resulting force-vector
2. if the anchors are strongly pretensed, they belong straight, and the friction takes the the force, because
there is a multdirectional stress state.
the german building codes allow to calculate this in that way.
i recommend a shear lug on the base plate to transfer shear. aisc design guide 1 has guidance for designing these.
if relying on anchor bolts, it has to be considered that the holes for the anchor bolts will be oversized. to count on all of the anchor bolts you'll need plate washers with standard holes that are field welded to the base plate.
if this is for a job in the us, i wouldn't rely on what a foreign code says.
correct me if i'm wrong, but pretensioning will not reduce the breakout cone or required development length.
as for codes, would you go to a doctor who would only treat you with procedures from a manual? no, we rely on doctors to use knowledge and reason.
for a given embedment depth, i believe pretensioning will reduce the tension that can be imposed on the anchor rod and here is why.
for a given embedment depth, the concrete breakout has a specific value, which we'll call z for this case. you can reach z simply by pretensioning the anchor rod without ever having the column apply a load to it.
i don't think it is realistic to believe you can apply a tensile load to the anchor without having it affect the additional load that can be applied before the concrete breakout occurs. does the concrete know whether that load is coming from uplift on the column of pretensioning of the anchor rod? i don't think so.
based on that reasoning, i think that if you need to pretension the anchor rods to some force y, then the most you can count on the anchor rods for (for uplift from the columns) is z-y. this is only for the limit state of concrete breakout. i know that high strength steel bolts do not require a reduction in capacity for pretensioning, i am not sure if that carries over into anchor rods or not.
streit, you're describing a situation that stumped me and most of my colleagues at one time or another. the pretension force in the rod is an internal force. you can add external tension on the rod up to the pretension force without adding any more tension to the concrete cone. the pretension is resolved through concrete interlock at the bottom of the anchor rod and bearing of the nut (or whatever) against the concrete (or plate or whatever) at the top of the rod. any tension applied to the end of the rod, above the nut, would reduce the clamping force between the nut and the concrete, but it doesn't change the force on the concrete cone below, until the applied tension meets and exceeds the pretension force.
why would a wedge form in the concrete? why not just rely on the dowel action in the bolts or perhaps bending? if base plate is embedded in a concrete slab then tieing the base plate to the slab would avoid the problem.
are you using the aci shear friction method? i watched an aisc seminar where the presenter recommended using the shear friction method instead of resorting to shear lugs.
nutte, i agree that any tension applied to the rod above the nut would reduce the clamping force.
wouldn't the uplift imposed by the column be applied by the nut (through bearing on the baseplate), not above the nut? that is why i think it should be additive with the pretension force.
it's not additive. let's say you pretension 4 anchor bolts to 40 kips, each. this produces a compression force between the base plate and the concrete of 160 kips. now apply a 70 kip uplift to the column. the result is a 90 kip compression force between the base plate and the column. the bolts still carry 40 kips of tension, each. if you apply 160 kips tension, the clamping force goes to zero and the bolts still have 40 kips tension. if you apply 200 kips tension to the column, each bolt has 50 kips tension.
__________________
借用达朗贝尔的名言:前进吧,你会得到信心!
[url="http://www.dimcax.com"]几何尺寸与公差标准[/url]
huangyhg离线中   回复时引用此帖
GDT自动化论坛(仅游客可见)
 


主题工具 搜索本主题
搜索本主题:

高级搜索
显示模式

发帖规则
不可以发表新主题
不可以回复主题
不可以上传附件
不可以编辑您的帖子

vB 代码开启
[IMG]代码开启
HTML代码关闭

相似的主题
主题 主题发起者 论坛 回复 最后发表
shear key at base of walls huangyhg 产品功能分析 0 2009-09-15 09:43 PM
block shear vs. shear rupture at connections huangyhg 产品功能分析 0 2009-09-07 03:57 PM
base plate design ignores corners of base plate huangyhg 产品功能分析 0 2009-09-07 02:24 PM
base plate anchor rod hole size huangyhg 产品功能分析 0 2009-09-07 02:23 PM
【转帖】asme - where to star yang686526 American standards 0 2009-04-29 07:28 PM


所有的时间均为北京时间。 现在的时间是 11:30 AM.


于2004年创办,几何尺寸与公差论坛"致力于产品几何量公差标准GD&T | GPS研究/CAD设计/CAM加工/CMM测量"。免责声明:论坛严禁发布色情反动言论及有关违反国家法律法规内容!情节严重者提供其IP,并配合相关部门进行严厉查处,若內容有涉及侵权,请立即联系我们QQ:44671734。注:此论坛须管理员验证方可发帖。
沪ICP备06057009号-2
更多