默认 shearwall heigh

shearwall height
this is a pretty basic question about shearwall height. let's say i have a 1-story house with 8' stud walls. the framed wall rests on the floor system, which consists of 2x12 joists (see attached .jpg file for a cross section).
for the shearwall height, do i use 8' or 8'+ depth of the floor?
quote:
for the shearwall height, do i use 8' or 8'+ depth of the floor?
in what context? what are you attempting to do? depending on what you are doing, it could be either.
ba
hi ba,
for example:
1) checking the maximum height to width ratio for shearwalls (ibc table 2305.3.4)
2) calculating the load/ft to the roof diaphram (do i use 8'/2*wind pressure, or 9'/2*wind pressure).
3) calculating the holddown loads: (unit shear) x (wall height)
thanks for your help.
it's to the top of the foundation, 8' + floor, section 2305.3.5. why is the wall resting on the 2x12? seems to me to be a waste.
hi sandman,
i found the section in the ibc that you referred to - the shear wall height is defined as:
1. the maximum clear height from the top of the foundation to the bottom of the diaphragm framing above.
for reference, i've attached the figure from the ibc.
maybe i'm mistaken, but "clear" height would seem to mean from the top of the floor sheathing to the bottom of the diaphragm framing above. if you look at the 2nd story in the figure, the clear height goes from the floor diaphragm below to the bottom of the framing above. i guess my confusion is this:
for the shearwall height of the 1st story - do you measure the height from the mudsill that rests on the foundation, or from the 2x plate that the wall studs rest on?
also, i don't understand your comment about the wall resting on the 2x12 being a waste.
1: per the diagram to the underside of the floor/roof diaphragm framing... i.e., to the top of the associated double wall plate.
2. 9'/2, but this would be for a single story structure. for a multi-story structure, it is the distance between the floor/roof diaphragm plywood above and the floor diaphragm plywood below divided by 2.
3. diaphragm plywood to top of concrete foundation wall or footing.

mike mccann
mmc engineering
hi mike,
thanks for your answer... i'm not quite clear on number 1: for checking the maximum height to width ratio, would i use 9' as well? [9'=from the top of the stem wall to the top double plate, or 8'=from the top of the floor joists (diaphragm) to the top double plate]. please see the picture i attached in my first post - do i measure the height for the ratio from the top of the foundation stem wall, or from the top side of the joists (where the wall studs rest)?
thanks for your help.
the code seems to be addressing how the sheathing will react to lateral loads. it requires that your shearwall segments act like deep beams with, what i would think, is a very stiff wall section. this exercise is intended for determining the maximum lateral shear your wall will take. this section should not be used for addressing how your loads (wind and seismic) are distributed to the diaphragms or how you will need to anchor your shear wall.
ex. using this calculation i can determine that wall a can resist ## kips of lateral shear. i only need it to resist # kips. ok, i do not need another shear wall in this direction, now i will design the connections.

i have a wall that has a lot of windows in it. i'd like to use as many of the full height wall segments as possible for shear walls, but i need to check that they meet the height to width requirement. so my question is: when checking this ratio, do i use 9' (from the top of the stem wall to the top double plate), or 8' (from the top of the floor joists and sheathing where the the studs rest, to the top double plate).
my thought is that the latter height (8') is actually the "clear height."
short answer - 8'
for all intents and purposes, the top of the floor acts as a fixed base and the bottom of the next floor's joists act as a fixed top. the shearwall is then checked for empirical stiffness.
quote:
1) checking the maximum height to width ratio for shearwalls (ibc table 2305.3.4)
2) calculating the load/ft to the roof diaphram (do i use 8'/2*wind pressure, or 9'/2*wind pressure).
3) calculating the holddown loads: (unit shear) x (wall height)
i am not familiar with the named code, but i believe:
1) use clear height for h/w ratio.
2) use clear height/2 plus roof thickness plus parapert height.
3) use total height above concrete foundation for holddown loads.
at least, that is the way which makes sense to me.
ba
__________________
借用达朗贝尔的名言:前进吧,你会得到信心!
[url="http://www.dimcax.com"]几何尺寸与公差标准[/url]
huangyhg离线中   回复时引用此帖
GDT自动化论坛(仅游客可见)
 


主题工具 搜索本主题
搜索本主题:

高级搜索
显示模式

发帖规则
不可以发表新主题
不可以回复主题
不可以上传附件
不可以编辑您的帖子

vB 代码开启
[IMG]代码开启
HTML代码关闭

相似的主题
主题 主题发起者 论坛 回复 最后发表
shearwall footings huangyhg 产品功能分析 0 2009-09-15 10:08 PM
masonry shearwall heightlength ratio huangyhg 产品功能分析 0 2009-09-10 12:50 PM
masonry shearwall - 2 story with perforations huangyhg 产品功能分析 0 2009-09-10 12:49 PM
ibc code approval of shearwall huangyhg 产品功能分析 0 2009-09-09 06:47 PM
8 conc. shearwall boundry condition huangyhg 产品功能分析 0 2009-09-07 08:57 AM


所有的时间均为北京时间。 现在的时间是 10:48 AM.


于2004年创办,几何尺寸与公差论坛"致力于产品几何量公差标准GD&T | GPS研究/CAD设计/CAM加工/CMM测量"。免责声明:论坛严禁发布色情反动言论及有关违反国家法律法规内容!情节严重者提供其IP,并配合相关部门进行严厉查处,若內容有涉及侵权,请立即联系我们QQ:44671734。注:此论坛须管理员验证方可发帖。
沪ICP备06057009号-2
更多