几何尺寸与公差论坛------致力于产品几何量公差标准GD&T (GDT:ASME)|New GPS(ISO)研究/CAD设计/CAM加工/CMM测量  


返回   几何尺寸与公差论坛------致力于产品几何量公差标准GD&T (GDT:ASME)|New GPS(ISO)研究/CAD设计/CAM加工/CMM测量 » 三维空间:产品设计或CAX软件使用 » CAD设计 » 产品功能分析
用户名
密码
注册 帮助 会员 日历 银行 搜索 今日新帖 标记论坛为已读


 
 
主题工具 搜索本主题 显示模式
旧 2009-09-15, 10:55 PM   #1
huangyhg
超级版主
 
huangyhg的头像
 
注册日期: 04-03
帖子: 18592
精华: 36
现金: 249466 标准币
资产: 1080358888 标准币
huangyhg 向着好的方向发展
默认 single bolt connections in steel frames

single bolt connections in steel frames
there has been a lot of discussion at our office over the use of single bolt connections in steel frames that we design. the two more experienced people feel quite strongly that you should not design a bolted connection that uses only one bolt. one claims that it is an erection safety issue. the other states that a single bolt connection has more prying force applied to it when the connection is in compression. unfortunately, we cannot find any piece of code which states whether or not a single bolt connection is allowed.
has anybody else heard about this rule? what is the background/ reasoning for not using a single bolt connection in a steel frame?
check out our whitepaper library.
single bolt steel connections are bad engineering practice.
they should only be used under extremly light loads and i mean
like 500 lb. they are bad simply from a redundancy point of view. you never want to have a connection that will fail if one bolt is loose or damaged. they are right it is also an erection hazard you need one hole for a drift pin and one to hold the bolt you put in to take the drift pin out
one bolt connections is just real bad practice. rotation of a beam can easily occur. use a min. of 2 at all times. good luck.
this issue has surfaced several times in my career. the philosipy of my mentors and now my own has been that this is bad engineering practice. if you reference aisc manual of steel construction (at least he asd additions) they do not include in their tables tabulated values for a single bolt connection. also in the aisc manual (one edition at least) there is an illustration that shows a connection where there is a horizontal row of (2) fasteners in the supported member. you could rationalize that the load was to great for a single fastener so they put (2) and that the depth of section limitation forced them horizontal. or you could rationalize that even though the load was not great and therefore the section chosen lacked depth that a minimum of (2) bolts is required and therefore forced the horizontal placement.
with all that said, i came to a personal conclusion that the supported
let me throw my two cents in.........
single bolt connection........bad......
two or more bolt connections............good.
i like to sleep nights when i'm not working.
umgrego2,
you are in fact right. there is no piece of code that is known to exist that directly specifies you must use at least two bolts in the connections. there are not so obvious reasons in all phases of steel construction why a minimum of two bolts (2 lines of bolts in beams) should be used. the steel code book addresses steel construction in all phases of steel construction. if you are a design engineer you are responsible for the reasons that impact only the design of the structure and nothing more. one example is to look at the entire mechanics of a typical beam end connection.
a beam end connection is either framed into a web or a flange of another structural member. when it's framed into the flange of say a building column the connection undergoes both shear and prying forces. shear is the obvious load the connection must resist. the prying force is the load condtion that is often mis-understood. it is best describe as a moment whose axis is half way between the center of the column and the column flange where the beam connects. the moment's value is the the beam end reaction times the distance from the column flange to the column center.
the prying force is ususally the beam-end reaction times the distance to the column center.the prying force must be resisted by either the end connection or the column itself.
if you decide to let the column resist the moment then the column must be designed to resist this moment at every area where a beam connects into a flange in addition to it's other design parameters for the column application. now your beam end connection can be a simple shear single line connection located at the beam center without no design for prying due this moment. if a beam connects to a column web then there is no moment and therefore there is no prying action at this type of end connection. it's just shear.
if you design building column(s) to be the structural element that resists end connection prying you can see how cumbersome it will be since some beams frame into the column flange and some beams connect to the column web most having different end reactions producing different moments at different points along the length of your column(s). all of this just because you want to use a single line of bolts on every beam.
thank god for the invention of the multi-line beam end connection!. if the end connection is used to resist the moment then a single line of bolts located at the beam center will not resist prying. the moment is resolved into both the tension and compressive forces. these forces depend on the placement of your of your bolt lines.
the tension is what is commonly called the prying force because it's located above the neutral access of the beam and wants to pull away from the column while. the centroid of your multi-line bolt group is placed at the center of the beam with the top bolts resisting tension (prying) and shear. the bottom portion of the bolt group resists only shear. the compressive force is applied directly to the column flange from the connection angles. again if the beam connects directly to the web of the column there is not prying moment or forces.
as you can see it is much easier to make standard tables and standardize end connections for the beam end connection to resist the required prying loads. in multi story buildings it's just not pracitcal to design the columns for this.
above is an example of why beams normally use at least two-lines of bolts but what about simple tension and compression members such as knee bracing where one bolt is sufficent from the design stand point?
lets look at the actual erection of the element. if you take note on how most iron workers first align the holes when bolting up the connection you will notice they use a spud wrench. a spud wrench is a solid, long, and tapered rod that has an open-end wrench on the other end. they place the tapered end of the wrench into one of the bolt holes to align the connection. once one of the other open bolt holes is close to being align they will place the bolt in it and pull the wrench out from the first hole. they will then place a bolt in the first hole and place the buts and washers on both bolts. they flip the spud wrench around and use the open end to snug type both nuts. the iron worker will move and go on to the next piece that needs to be erected and do the same. the key in erection is to keep the crane moving and reduce the time it takes for the iron worker to stabilize the connection. placing only one bolt hole (or bolt line) makes alignment & stabilization much more difficult for the iron worker. you have to re
thanks to everyone for your thoughtful replies.
just to let you know what my other research has provided:
the cisc responded with:
"from an erection consideration perspective, 2 bolts are the minimum required for installation purposes. within the industry, there has always been a general rule of 2 bolt minimum for any structural connection."
however, the reply i got from the aisc referred to osha standards:
"you will want to check the federal register, as osha does have some rules regarding the number of bolts that must be in place before a structural
more specifically (direct from osha):
1926.756 beams and columns.
(a) general. (1) during the final placing of solid web structural members, the load shall not be released from the hoisting line until the members are secured with at least two bolts per connection, of the same size and strength as shown in the erection drawings, drawn up wrench-tight or the equivalent as specified by the project structural engineer of record, except as specified in paragraph (b) of this section.
(2) a competent person shall determine if more than two bolts are necessary to ensure the stability of cantilevered members; if additional bolts are needed, they shall be installed.
umgrego2
since it is "standard practice" to use at least two bolts, you will lose in court if you use fewer.
also, per krus1972's accurate erection discussion, any money saved in fewer bolts and holes will be spent in longer erection time so there is no economic reason to do so.
everyone seems to be talking about beam-to-column connections. sometimes we design frames with knee braces (or kickers) where the
my humble point of view that single bolt, even if it is adequate by calculations, is very bad practice. we are not talking about huge expense but we buy a lot of insurance. another thing that i always do is use minimum of 3/4 inch diameter bolts in my structural frames.
this is my two cents worth.
__________________
借用达朗贝尔的名言:前进吧,你会得到信心!
[url="http://www.dimcax.com"]几何尺寸与公差标准[/url]
huangyhg离线中   回复时引用此帖
GDT自动化论坛(仅游客可见)
 


主题工具 搜索本主题
搜索本主题:

高级搜索
显示模式

发帖规则
不可以发表新主题
不可以回复主题
不可以上传附件
不可以编辑您的帖子

vB 代码开启
[IMG]代码开启
HTML代码关闭

相似的主题
主题 主题发起者 论坛 回复 最后发表
rotation in cold-formed steel moment connections huangyhg 产品功能分析 0 2009-09-15 07:35 PM
odd beam to column connection 9steel0 huangyhg 产品功能分析 0 2009-09-10 04:54 PM
base plate thickness and bolt preload huangyhg 产品功能分析 0 2009-09-07 02:27 PM
add steel base plate for new column to existing post-tension huangyhg 产品功能分析 0 2009-09-07 10:10 AM
【转帖】asme美国机械工程师标准目录2 huangyhg American standards 5 2009-04-26 02:38 PM


所有的时间均为北京时间。 现在的时间是 12:20 AM.


于2004年创办,几何尺寸与公差论坛"致力于产品几何量公差标准GD&T | GPS研究/CAD设计/CAM加工/CMM测量"。免责声明:论坛严禁发布色情反动言论及有关违反国家法律法规内容!情节严重者提供其IP,并配合相关部门进行严厉查处,若內容有涉及侵权,请立即联系我们QQ:44671734。注:此论坛须管理员验证方可发帖。
沪ICP备06057009号-2
更多