几何尺寸与公差论坛------致力于产品几何量公差标准GD&T (GDT:ASME)|New GPS(ISO)研究/CAD设计/CAM加工/CMM测量  


返回   几何尺寸与公差论坛------致力于产品几何量公差标准GD&T (GDT:ASME)|New GPS(ISO)研究/CAD设计/CAM加工/CMM测量 » 三维空间:产品设计或CAX软件使用 » CAD设计 » 产品功能分析
用户名
密码
注册 帮助 会员 日历 银行 搜索 今日新帖 标记论坛为已读


回复
 
主题工具 搜索本主题 显示模式
旧 2009-09-15, 11:04 PM   #1
huangyhg
超级版主
 
huangyhg的头像
 
注册日期: 04-03
帖子: 18592
精华: 36
现金: 249466 标准币
资产: 1080358888 标准币
huangyhg 向着好的方向发展
默认 site inspections of concrete structures

site inspections of concrete structures
how accurate (rigorous) should we be with site inspections of concrete structures? my question concerns, bar lengths, concrete cover, hairpin ties size, etc.
rigorous? it's either right or not (with tolerances, of course). if you are asking about frequency, it depends on the criticality of the structure and the diligence of the contractor. i usually start out checking everything, then back off a bit if i see that the contractor is doing a good job. i also select areas of the construction to give a good check, while doing a cursory check on others. this introduces a bit of randomness to the process without having to measure each rebar spacing, cover, etc.
documentation is important. if you find something, write it down. keep a "non-compliance" list and delete the items as they are corrected.
if you are the engineer of record, or if you have responsibility for compliance, don't be shy. employ the authority of the local building official if necessary to get the project on course if you find deficiencies.
black and white - right or wrong. end of story.
great advice ron!
thanks ron and qshake, but i'm asking if i need to look at bar lengths or just count the number of bars and bar size in a beam for example?
thanks a lot
in some manner you need to check the bar length, splice lengths, etc. if bars are not hooked, development length can be critical, so a few inches makes a difference.
do you actually need to measure the length of the bar? not really...there are other ways to see if it is correct. where the bar terminates relative to the outside face of the form, for instance, tells you what you need to know.
one of the things we have to be careful of in our inspections is not to assume responsibility for items we cannot control. as an example,if you measure one horizontal control distance, are you expected to measure them all? it might then be assumed that you are responsible for horizontal location (different than horizontal distance).
our goal in the specific inspection is to see if we or the engineer of record got what was wanted, based on the filed or officially changed plans, specs, or code requirements.
when i do inspections, i check clearances, correct rebar (you'd be surprised how many contractors use #5's instead of #6's) at the correct spacing, lap distances, etc. obviously, you don;t have the time to check every clearance, spacing, etc. if the job was ok, then i would write in my inspection report something like "..the reinforcing steel spacing appears to be acceptable." the reason for "appears to be" is because of liability issues. unless you actually checked every bar, then you shouldn't write "...rebar is acceptable."
while at the site, check the formwork, afterall, that is important too. in doing so you will know the relative dimensions of the reinforcing laying inside from the clearance required. another good point by ron is the terminal ends especially at lap splices. always measure splices. since the bars are generally close enough you can evaluate the whole set rather than measure each one.
similarly, you can gauge the clearance by using a cheater. a cheater would be a piece of wood on a long stick (length as required). the length of the wooden end piece is the required clearance and you place the stick down the forms to quickly assess the areas of concern.
check bar ties as well. you don't want rebar moving all over when concrete is being placed.
and as mentioned above, do check bar size. many times the job is littered with bars of all shapes and sizes. not everyone is paying attention when they go and grab something!
agree with ron & qshake.
also, one concept that is not well documented is the difference between observation and inspection.
the purpose of observation is - to inspect to such a degree that the engineer has confidence that the plans and specs are being correctly interpreted and implemented into the construction. in other words: are you as an engineer successfully communicating to the contractor. by reviewing rebar (perhaps to the extent that ron suggested) do you begin to have confidence that the contractor has the ability, knowledge and know-how to correctly interpret all the other beams/details that you indicate.
liability under observation: did you have reasonable evidence to suggest that the contractor had the ability to interpret your plans? it then remains the contractor's responsibility to ensure that the bars are all in place correctly.
the purpose of inspection is not an attempt to determine the efficiency of your communication, but rather to exhaustively check all the work.
liability under inspection: all yours.
jae, thanks for that helpful reminder on the difference...very important stuff.
__________________
借用达朗贝尔的名言:前进吧,你会得到信心!
[url="http://www.dimcax.com"]几何尺寸与公差标准[/url]
huangyhg离线中   回复时引用此帖
GDT自动化论坛(仅游客可见)
回复


主题工具 搜索本主题
搜索本主题:

高级搜索
显示模式

发帖规则
不可以发表新主题
不可以回复主题
不可以上传附件
不可以编辑您的帖子

vB 代码开启
[IMG]代码开启
HTML代码关闭

相似的主题
主题 主题发起者 论坛 回复 最后发表
concrete sampling guidlines huangyhg 产品功能分析 0 2009-09-08 12:34 PM
concrete roof slab load huangyhg 产品功能分析 0 2009-09-08 12:34 PM
concrete mix= reinfocing for exterior composit deck huangyhg 产品功能分析 0 2009-09-08 12:19 PM
concrete corrosion in partial saturated condition huangyhg 产品功能分析 0 2009-09-08 11:54 AM
chapter 4 preliminary design properties of concrete huangyhg 产品功能分析 0 2009-09-07 11:23 PM


所有的时间均为北京时间。 现在的时间是 11:12 AM.


于2004年创办,几何尺寸与公差论坛"致力于产品几何量公差标准GD&T | GPS研究/CAD设计/CAM加工/CMM测量"。免责声明:论坛严禁发布色情反动言论及有关违反国家法律法规内容!情节严重者提供其IP,并配合相关部门进行严厉查处,若內容有涉及侵权,请立即联系我们QQ:44671734。注:此论坛须管理员验证方可发帖。
沪ICP备06057009号-2
更多