默认 sizing a bearing plate for point load on concrete slab

sizing a bearing plate for point load on concrete slab
we use air pallets to move heavy loads, but when we set the load down it causes a point load on the concrete slab. the desire is to dissipate the point load by providing a metal plate to set the point load down on that would spread the load out over the concrete. the problem is calculating the size of the plate to use. we are considering using 1/8 inch thick steel plates. the point load is about 6000 pounds. the concrete is older 3000 psi compressive strength, no rebar.
i searched for a similar question, found a few, but none that was exactly like this. i also look at the formulas in x calcs, but couldn't find a match.
check out our whitepaper library.
you have 6000 pounds on each point or
6000 pounds total?
if the concrete is rated at 3000psi
then 1 inch square will withstand
3000psi. 2 inch square 6000psi etc.
you pick the safety factor.
thanks dimjim, seems a little oversimplified though. so what you are saying is if we put a sheet of .001 steel down that is 1 inch by 1 inch, we get the same result as 1/4 inch thick plate? i guess the question was not clearly stated. how do we determine the proper size and thickness of the metal bearing plate?
you really need to check the slab for bending and punching shear--dimjim is only considering bearing pressure, which won't control.
i use the method in pca's slab-on-grade design book.
daveatkins
to check bending in the slab, check out "designing floor slabs on grade" 2nd edition by ringo & anderson, p. 52.
steve
once you have checked the slab and assuming it works, then you can design your bearing plate per aisc specifications. the aisc manual of steel construction has design examples for this.
markk1pe:
i would check this bearing plate as base plate per aisc manual.
typically we simply the calculation by assuming the bearing cantilevers past the column and is loaded by the bearing pressure. this results in a simple cantilever model where your moment is wl2/2. you can then calculate the required section modulus and required thickness, if you know the allowable bending stress for your base plate material. it's not absolutely that simple but it's close. generally you find that as you increase the dimensions of the plate, the bearing stress goes down but the plate thickness goes up.
to assume that you have even pressure under the plate, the plate has to be thick enough that it acts as a rigid plate, not as a flexural plate, otherwise the bearing stress is not constant over the plate. if you assume equal pressure and base the design on stress then your starting assumption is wrong and the pressure near the centre will be much higher, especially if you use a sheet of .001 steel.
it is not sufficient to simply limit the stresses to normal stress levels, you need to limit the rigidity.
i would think that timoshenko would cover this.
is the problem the design of the base plate or the tensile stresses in the slab... i would typically use a plate 3/8" min. if it's the design of the slab, then the thickness of the slab, the subgrade modulus, the load and the spacing of the loads come into play. if you can provide spacing information and slab thickness, i can try to model it and give you an indication of what the concrete stresses would be.
dik
mark, you can size the pad however big you want depending how much pressure you want. the big question is, what is holding the pad? lets say you have 6"x6" pad, this pad is attached to what? 3x3 pipe? i dont know the pallete looks like. once you give me this information, i can give you the formula from aisc. so this is the info you need
1. size of pad you want
2. whats holdidng the pad (centered in the pad)
t min = l x sqrt(2pu/0.9 fy.b.n)
l= the cantilevered lenght, for example if you have 3x3 column on 6x6 pad, then your cantilevered length is 1.5"
pu=ultimal axial load
b= usually i use the symetrical column so the pad is symetric also. so b = n = dimension of pad
fy= steel strength
so for example i have 60kips on 3x3 column with 6x6 pad then my t min should be .373".
let me know if i did this correctly guys!
__________________
借用达朗贝尔的名言:前进吧,你会得到信心!
[url="http://www.dimcax.com"]几何尺寸与公差标准[/url]
huangyhg离线中   回复时引用此帖
GDT自动化论坛(仅游客可见)
 


主题工具 搜索本主题
搜索本主题:

高级搜索
显示模式

发帖规则
不可以发表新主题
不可以回复主题
不可以上传附件
不可以编辑您的帖子

vB 代码开启
[IMG]代码开启
HTML代码关闭

相似的主题
主题 主题发起者 论坛 回复 最后发表
how to thicken an existing concrete slab on grade huangyhg 产品功能分析 0 2009-09-09 05:54 PM
effects of a load on sog and below grade huangyhg 产品功能分析 0 2009-09-08 09:45 PM
crack in old floor slab huangyhg 产品功能分析 0 2009-09-08 02:20 PM
concrete roof slab load huangyhg 产品功能分析 0 2009-09-08 12:34 PM
bearing plate huangyhg 产品功能分析 0 2009-09-07 03:17 PM


所有的时间均为北京时间。 现在的时间是 02:08 AM.


于2004年创办,几何尺寸与公差论坛"致力于产品几何量公差标准GD&T | GPS研究/CAD设计/CAM加工/CMM测量"。免责声明:论坛严禁发布色情反动言论及有关违反国家法律法规内容!情节严重者提供其IP,并配合相关部门进行严厉查处,若內容有涉及侵权,请立即联系我们QQ:44671734。注:此论坛须管理员验证方可发帖。
沪ICP备06057009号-2
更多