几何尺寸与公差论坛------致力于产品几何量公差标准GD&T (GDT:ASME)|New GPS(ISO)研究/CAD设计/CAM加工/CMM测量  


返回   几何尺寸与公差论坛------致力于产品几何量公差标准GD&T (GDT:ASME)|New GPS(ISO)研究/CAD设计/CAM加工/CMM测量 » 三维空间:产品设计或CAX软件使用 » CAD设计 » 产品功能分析
用户名
密码
注册 帮助 会员 日历 银行 搜索 今日新帖 标记论坛为已读


回复
 
主题工具 搜索本主题 显示模式
旧 2009-09-16, 09:14 PM   #1
huangyhg
超级版主
 
huangyhg的头像
 
注册日期: 04-03
帖子: 18592
精华: 36
现金: 249466 标准币
资产: 1080358888 标准币
huangyhg 向着好的方向发展
默认 why provide negative reinforcement in footings

why provide negative reinforcement in footings?
i'm curious what other engineers do when designing footings. in our office the senior engineers usually always specify reinforcement in the top and bottom of footings when considering to uplift. regardless if the net effect is actually compression.i usually only specify bottom reinforcement if the net effect is compression. is this reasonable or should i specify both top and bottom?
two reasons. one is to guarantee that you have enough temperature and shrinkage steel. the other is to remove any confusion of the contractor whether he should center the one layer of steel or place it on the bottom. even an inept contractor knows that with two layers, one goes near the bottom and the other near the top.
anyone else have any?
calculor,
could you clarify just what you mean by "if the nett effect is actually compression"
if you are simply saying that you have a column base where the column is subject to uplift, but the total column_plus_ overburden load is downward, then the footing will be subject to negative bending, and your seniors are correct. [for that case, the nett upward pressure under the base (although positive) would be less than the downwards overburden pressure - hence top surface tension]
austim
you are right about the case of column uplift balanced by the foudation weight and overburden. negative reinforcement is essential in such case.
however, i feel that calculor does not mean that. we check for the gross bearing pressure (to be less than sbc) due to the total load at the footing base including the overburden and the footing weight. however, for design of the footing cross section, we calculate the bm and sf due to the net pressure which is gross pressure minus the pressure due to uniformly applied loads such as overburden and footing weight. (am i right calculor?)
if this net pressure is compressive, we get bm causing bottom tension only. we do not require top reinforcement for bending. however, if the section is thicker(>750mm.), we provide nominal mesh of reinforcemet at the top to take care of temperature and shrinkage stresses.
for less thickness of footing, there is no need of top reinforcement.
hi,
there is also an added adavantage of having a top reinforcement for a footing of reasonable depth in that the concrete is confined between top and bottom mats, and side face reinforcments(if provided) and its resistance to compression and (shear??!!) is increased not from structural view point but from performance point of view. in terms of it being more confined as well as ductile.
thus when u detail a reinforcement for an isolated footing especially if column loads are relatively high u provide it in form a cage!!!...a specific typical case....may be something like a pile cap detailing....
but bottom line is enhanced compression resistance and ductility
hope this argument should also make some sense!!
may be ...iam not sure...i would appreciate if some one has any comments in this regard
hope it helps
regds
raj
calculor may correct me if i misinterpretted his original question. i believe he is asking whether engineers specify top and bottom rebars for seismic column footings regardless of whether there is a net uplift or not.
more often than not, the downward force on a seismic footing due to proper load combination is larger than the maximum uplift on the same footing, thereby requiring, technically, less rebar at the top (sometiems none).
but it is common practice here in california to design the bottom bars and call out same number of bars at the top as well. this leaves less room for contractor to make a mistake. and it makes it obvious which footings are seismic and which are gravity only.
i think everyone has had good points so far. to add another from the practical standpoint, ya gotta tie the anchor bolts to something. it might as well be steel that you leave in place.
jim
jimparks,
do you mean the anchors from the columns be tied to the bottom bars with a standard hook?
in california (state projects and perhaps some local jurisdictions), the use of j bolts is prohibited. they recommend a headed bolt. sometimes, i elect to use uplift plates.
any comments on requirements from other parts of the us will be appreciated.
whyun,
do you know what the reasoning is for not allowing j bolts??
this isn't an area i work in often but i'm curious to hear the reasoning!!
---
andrew
i suppose they do not want a bolt heavily loaded in tension to "straighten-out". as it straightens, the concrete will crush near the inner radius of the bend.
i am not into testing or research so i am not sure whether this is a valid claim, but state of california thinks so.
with a headed bolt, supposedly, you can more reliably expect a cleaner shear cone.
for multiple bolts in a seismic column, often i tie the bolts together by using an uplift plate at the bottom using double nuts.
jedclampett, whyun,
ha ha that's a good one - that you detail top and bottom mats because contractors wouldn't know where to put a single mat.
__________________
借用达朗贝尔的名言:前进吧,你会得到信心!
[url="http://www.dimcax.com"]几何尺寸与公差标准[/url]
huangyhg离线中   回复时引用此帖
GDT自动化论坛(仅游客可见)
回复


主题工具 搜索本主题
搜索本主题:

高级搜索
显示模式

发帖规则
不可以发表新主题
不可以回复主题
不可以上传附件
不可以编辑您的帖子

vB 代码开启
[IMG]代码开启
HTML代码关闭

相似的主题
主题 主题发起者 论坛 回复 最后发表
minimum reinforcement on grade beams huangyhg 产品功能分析 0 2009-09-10 02:16 PM
maximum spacing of reinforcement in footings huangyhg 产品功能分析 0 2009-09-10 01:24 PM
load redistribution on a line of footings supporting continu huangyhg 产品功能分析 0 2009-09-10 11:10 AM
development of flexural reinforcement in footings and pile c huangyhg 产品功能分析 0 2009-09-08 06:31 PM
bottom longitudinal reinforcement at supports for simply sup huangyhg 产品功能分析 0 2009-09-07 04:31 PM


所有的时间均为北京时间。 现在的时间是 09:25 PM.


于2004年创办,几何尺寸与公差论坛"致力于产品几何量公差标准GD&T | GPS研究/CAD设计/CAM加工/CMM测量"。免责声明:论坛严禁发布色情反动言论及有关违反国家法律法规内容!情节严重者提供其IP,并配合相关部门进行严厉查处,若內容有涉及侵权,请立即联系我们QQ:44671734。注:此论坛须管理员验证方可发帖。
沪ICP备06057009号-2
更多