默认 working loads vs limit state loads

working loads vs limit state loads
hi, i am doing some research on membrane structures (architectural sails) and have come across some information that says that these type of structures (large displacement structures) should be analysed at working loads, not limit state loads. it says that low factors of safety may result if an ultimate limit states design methodology is used. firstly what is the definition of working loads compared to limit state loads, and secondly why is this so?
check out our whitepaper library.
if you have a read of 'cable structures' by max irvine section 2.7 (a classic book) it will answer your question. sorry for the very quick answer - i'm pushed for time. come back if you want further thoughts.
good luck
it takes an oddy to answer this one! here is my version to attract further discussions.
working load design was the standard in the past but limit state design took over some 30 years agao.
with working load the actual load on the structure is used and the method of analysis is based on the elastic hehaviour of the material. the design is control by using a specified limit of the stress. the margin between the maximum stress at failure to the specified limit is the safety factor, approximately about 2 in many structural designs. it is simple and served us well.
limit state design is an attempt to bring the engineer's attention to the limit state of the materialand to convince us that it is safe to use the inelastic part of the material if we are sufficiently far away from the maximum limit at the failure point. to do this we have a safety factor for the material and also a safety factor for the load. the safety factors are statistically determined. in limit state design one uses the actual stress-strain curve of the material and the
most lrfd (limit state) bridge designs also require "serviceability" (service or working)checks.
these structures are designed to sustain certain factored load cases without failing, although the factored loads may cause some permanent deformation (for extreme cases such as seismic load cases).
the serviceability checks include fatigue, cracking, and deflections due to nominal loads which are meant to be comparable to the loads that we expect the structure to experience often during the serviceable life of the structure (i.e. a service live load is often in psf, but most live loads are actually discreet loads - closer to point loads).
with "limit state" design, we're not usually concerned with the amount of deflection, but with the overall capacity of the system with respect to failure or collapse.
with "working stress" design, we're concentrating on wholly "elastic" behavior and the utility of the structure during it's useful life.
although i'm not very familiar with design of membrane structures (my shells course was long ago - and so far never used), i suspect that if deflection is a primary concern, then working stresses would give higher safety factors.
perhaps i too will get a copy of the book that was referenced by jwb46 above.
good luck.
both of the above posts have stated that limit state design uses materials beyond their elastic range. this is true sometimes, but not always. aisc lrfd is a limit state design for steel and many, many designs of beams will end up defining the limit state as the yield point.
in other words, the factored loads are used to find a beam that will just yield....not go beyond yield into the plastic zone. so the limit state can be defined and is defined many times as the elastic limit.
working stress design and limit state design (or lrfd) really do the same thing, its just that the working stress method uses a set, somewhat arbitrary (based on experience and judgement) safety factor. lrfd uses safety factors based on statistical probability of failures so are less arbitrary except for the unpleasant fact that current specs like aisc lrfd have set load factors and phi factors to create a probability of failure similar to the traditional working stress methods.
for a big sail type structure, the designation you refer to about using working stress design is puzzling. both methods design for similar probabilities of failure and both methods will required checks of deflections (servicability) at non-factored load conditions.
why they would figure that limit state methods would create a lower safety factor does not sound logical. in fact, using lrfd for a structure primarily loaded with wind may actually provide a higher safety factor as the load factors are adjusted to account for the variability of the load and wind is highly variable.
the asce 7 load factors provide the following safety factor: 1.6 load factor and assume 0.9 strength reduction factor:
1.6 / 0.9 = 1.777 safety factor for lrfd
for working stress: roughly 1/ 0.6 = 1.666 safety factor for working stress (1/3 stress increase no longer valid)
i am concious of the fact we are engineers from different background and different countries but in reinforced concrete design the ultimate limit state is when concrete reaches a compressive strain of 0.0035 (in european countries, the usa practice uses 0.003 i think) and the reinforcement can be stressed well beyond the yield point.
one thing is certain - at ultimate limit state the structure is not considered serviceable.
rowe covered the serviceability limit state very well. i have written a few words on it but refrained from putting them forward in my first response, for afraid of confusion. from stress analyses of reinforced concrete i find the serviceability state generally differs very little from the solution by working load approach based on elastic analysis. this is because at service condition we often use unity for the load factor and seldom load the structure significantly to pass its elastic range. i feel a need to defend the working load approach because of its association with the elastic or linear stress-strain concept. like rowe said it concentrates on the utility of the structure during it's useful life and therefore directly relevant. in my understnading, an engineer attempting to analyse a member loaded beyond its inelastic limit must be first able to solve the same problem when the stress is in the elastic range.
both working load and limit state load methods of design are just means to size up the members. with the former we can do it quicker while the latter keeps us in check more with reality (like knowing statistics, limits of the material etc). in term of analysing the structure we are still using the liner and elastic theory all the time (i.e. we can put 100 times more load and the computer returns 100 times more deflections and member forces. unless the engineer uses his brain he would not know the structure has failed or not.
it would appears that the sail structure mentioned by axle will require large deflection theory which is simply to calculate the equilibrium condition after the the structure has been loaded. this can be achieved by performing the analysis iterativelly by additing deflection to the no-load geometry until the deflection converges. for expedency engineers analyse a structure primarily with the equilibrium calculated at the "no load" configuration. this simplification generally works satisfactorily as serviceable structures rarely can deflect by more than 5%, unless it is something like the wall of a rubber tyre. thus i would describe the sail structure problem as nonlinear-elastic (geometry nonlineear while material elastic). if limit state design is applied then the full analysis should be nonlinear-inelastic. a further complication of the sail structure is that some materials could have strength in tension only (like cable and fabric) and repetitive analyses are needed to ignore
i don't know more about shell structures, but i want to mention about limit state desing and rc structures.i think lsd method is the best for rc structures. because you don't have to calculate some stress values in the material which is not very homegenous compared with many other structural materials.working load method is better for steel structures since in this case the calculated stress values are much more close to the real stresses occured in the material.besides the non-homegenty of the material,also its inelasticity (probably this is the most important ) make us be suspicious about our desing in which we assume concrete elastic(workind load case).
regards
thank you all for your comments. as a young engineer (only a year out of my studies) i am finding that most of the standards or textbooks i come across seem to be written in a way that makes it very hard to understand unless you have some prior knowledge of the subject or an expert on hand to assist you. i would have thought that they would be written in a way so that anyone could decipher the author鈥檚 intentions.
from your comments i think that i now have a clearer picture of the differentiation between working loads and limit state loads. however i would just like to verify a few points.
firstly, are the loadings that were used in a working load design the same as that, that are prescribed in current versions of the relevant standards. for example could i use a live load as listed in as/nzs 1170.1: 2002 鈥?structural design actions, part 1: permanent, imposed and other actions (being from australia i will reference australian standards in my questions) to carry out a working load design. obviously no load factor would be applied to this load when carrying out the design. in the case of wind loadings, as 1170.2 鈥?1989 gives a basic wind speed value vp (the p referring to permissible stress). in relation to as 1170.2 鈥?2002 this corresponds to a recurrence interval of 50 years. am i right to assume that to obtain the working loads on a structure in relation to wind, one would just follow the procedure prescribed in as 1170.2 using a basic wind speed equal to vp or a recurrence interval of 50 years.
secondly, in order to carry out the design of a member in accordance with working load theory, the current relevant standards cannot be used as the equations that are presented in them deal with the inelastic behaviour of the member. for example you could not simply just calculate the
hello axle
interesting topic, and fills in quite a few gaps for me. i'd be particularly interested in any response regarding your first point "firstly, are the loadings that were used in a working load design ...".
i stand to be corrected, but i think the scheduled ultimate ls windloads are different (greater) than those used in the old safety factor days, so i don't think one can simply interchange the wind speeds. i'm not sure if this is exactly what you are looking to do, but thought it worth a mention.
i'll keep an eye out for more responses!
bill
hi axle,
not sure if i can help much but this is my attempt below.
i am not a regular user of australian codes but the loads published in a design code are "design loads" for a structure to withstand in service. they are the working loads as long as i have been involved. this applies to the wind even if its magnitude occurs once every 50 years. it is a common practice to define a basic wind speed with occurrence once in 50 years at a specified terrain generally at 10m above ground measured as either a 3-sec maximum gust or an average over a longer duration. however for the working condition a 鈥渄esign鈥?wind speed must incorporate other factors (reflecting the structure's height, shape, importance etc) into the basic wind speed. i expect this to be fully documented in the code.
on the section capacity calculation you should find earlier codes based on elastic design helpful. they also provide the permissible limits for the stresses.
lastly on the selection of design parameter i can't help you as i need the document and time, both of which i do not have. however when dealing with such a problem one can always carry out a sensitivity study to see the effect of the selecting available choices and then make some sense out of the exercise. it may be the case the difference is not great enough and designing for the worst case can protect you. the behaviour of your sail structure may lie outside the bounds of the design code and you must approach it with an open mind.
i believe an accurate understanding of the structural behaviour of the sail structure is central to the design and for that you may need access to some specialised software which can analyse the structure interactively. basically the sail equilibrium condition must be computed at the deflected configuration and you may need to remove members in compression from the structure if they are tension-only elements. thus the expel-wind case can be simulated by reversing the wind direction.
on the large deflection of the column is ok i think nobody here can agree to that because a large deflection creates a large moment arm for the axial load and could be dangerous to the column. in your case you actually use it as a beam, even if it is place vertically, for supporting the sail structure and the column may even be in tension. thus large deflection may be acceptable in practice in your case. anyway i can confirm that if you calculate the equilibrium at the deflection configuration then your column will be safe even with large deflection.
i did a undergraduate project on nonlinear analysis and found the large deflections can be solved by at least three alternatives:-
(1) using linear software that designer uses (except specialists with particular applications), which compute the equilibrium condition at no-load configuration, and feed the deflection to the original geometry to recalculate until the deflection converges to an acceptable limit. this approach work well with the least amount of work. from my previous experience between 5 to 6 iterations should be suffice. you can simply write a post-processor by adding the linear portion of the delection (ie. dx, dy and dz) to original nodal coordinates. by comparing the sum of the squares of the deflection of any two successive runs you will be able to see where the solution is likely to be.
(2) adjust the element matrix with the stability functions. the stability functions are axial load dependent thus making the element less stiff if carrying a high axial load or become more stiff when under tension. for line elements the stability functions are well documented e.g. in coates, coutie and kong's book "structural analysis". i do not have information on the equivalent for the plate elements for your sail structure. one need access to the analysis software for this approach. two iterations are needed with the first one to provide the axial load data.
(3) using large deflection theory 鈥?this is a common method by adding a second order term to the element matrix. again i dealt with only line elements in my project and two iterations similar to (2) above are needed. some specialised software, claiming able to cope with large deflection, will have this built into the code.
the accuracy of all three methods is comparable and i didn鈥檛 find any one stood out better than the rest when i programmed them. i used them on both compressive ( to find out collapse) and tension (to investigate stiffening effect)
i haven't read much that i agree with yet.
concrete is not designed with limit state design (lsd). it is designed with ultimate strength design (usd). there is a huge difference. steel lrfd is not a limit state design. lsd in steel is more like full plastic design. lsd in concrete is a upper limit and results in more strength.
basically, lsd is an upper failure limit of which steel or concrete design does not recognize. lsd is only significant in failure analysis, and depends greatly on boundary conditions of element in question.
if the original post was refering to working stress design (wsd) vs ultimate strength design (usd), then most of the information above is correct if you remove the limit state wording and replace it with ultimate strength wording.
it seems a lot of people love to read their own posts.
__________________
借用达朗贝尔的名言:前进吧,你会得到信心!
[url="http://www.dimcax.com"]几何尺寸与公差标准[/url]
huangyhg离线中   回复时引用此帖
GDT自动化论坛(仅游客可见)
回复


主题工具 搜索本主题
搜索本主题:

高级搜索
显示模式

发帖规则
不可以发表新主题
不可以回复主题
不可以上传附件
不可以编辑您的帖子

vB 代码开启
[IMG]代码开启
HTML代码关闭

相似的主题
主题 主题发起者 论坛 回复 最后发表
working is other state huangyhg 产品功能分析 0 2009-09-16 11:27 PM
unfactored column loads huangyhg 产品功能分析 0 2009-09-16 05:12 PM
ransient loads huangyhg 产品功能分析 0 2009-09-16 03:35 PM
limit state vs working stress design huangyhg 产品功能分析 0 2009-09-10 10:36 AM
intl bldg code wind loads huangyhg 产品功能分析 0 2009-09-09 09:19 PM


所有的时间均为北京时间。 现在的时间是 01:56 PM.


于2004年创办,几何尺寸与公差论坛"致力于产品几何量公差标准GD&T | GPS研究/CAD设计/CAM加工/CMM测量"。免责声明:论坛严禁发布色情反动言论及有关违反国家法律法规内容!情节严重者提供其IP,并配合相关部门进行严厉查处,若內容有涉及侵权,请立即联系我们QQ:44671734。注:此论坛须管理员验证方可发帖。