10psf wind load
i asked some brief questions about this issue in the past and several of you responded, which i appreciate. i've been challenged on this another way now and would like your feedback.
is it possible to make the average wind pressure equal to 10psf and meet the requirements of section 6.1.4.1 of asce 7? for example, let's say we have a 10' tall building with a 10' projected roof area. if the wall pressure was designed for 15psf and the projected roof area designed for 5psf, would that be acceptable?? or does 10psf need to be applied uniformly across the entire vertical projection?
thanks.
if the areas are the same above and below the plate line, i guess that would work. but that would be a special case.
this is a moot point though, because i believe there is a 10 psf minimum for the projected area of the roof anyway, when e through the end are zero.
mike mccann
mccann engineering
i do it by applying both the exact wind pressure on the projected area and then comparing my different reactions (at the diaghragm above and below) and if either of them is less than applying 10 psf on the entire projected area, you use the 10 psf reaction(s).
akastud
for mwfrs:
"the wind load to be used in the design of the mwfrs for an enclosed or partially enclosed building or other structure shall not be less than 10 lb/ft^2 multiplied by the area of the building or structure projected onto a vertical plane normal to the assumed wind direction."
so splitting up the wind as 5psf on the upper part of the projection and 15psf on the lower does not seem to me to meet the intent. what if you concentrated 100psf in the first 2 feet and applied 0psf over the rest of the frame. would that seem acceptable?
additionally, don't forget about the "2a" distance from the ends where the locally higher loads have to be applied. unless you are conservative with your estimate, i would not average on thinking this thru more. there are too many variables here. take the more exact approach.
mike mccann
mccann engineering
if the more exact approach leads to a net load less than the 10 psf on the total vertical projection then 10 psf still controls.
i agree with haynewp. check what happens using, for example, 8.5 psf on typical walls, 12.8 psf at corners, and 0 psf on the roof (example only--you must use the correct loads for your situation). then check 10 psf on the entire wall and roof. see what controls.
daveatkins
thanks to each of you for your replies. here is my dilema. i do mostly single story buildings with 3.5/12 roof pitches. the 10psf nearly always controls, by a large margin. the problem we're having is trying to figure out how a competitor is seemingly ignoring the 10psf provision, and the prospective client doesn't care. so....giving our competitor the benefit of the doubt, we're trying to determine if we're looking at 6.1.4.1 incorrectly.
doesn't sound like we are. what recourse do we have? we are going to be priced higher because we're following the codes/standards, and our competitor isn't, and he's going to get the job. i'm not going to bend rules just to get a job, but an unlevel playing field is no fun to play on. that is why i want to make sure i'm thinking about this section of the standard correctly.
haynewp took my proposal to the extreme, which really helps flush out how best to look at it, and really points to the fact that it probably ought to be evenly distributed from top to bottom.
thanks again for each of your posts!!!
i see the dilemma, postframese, but what difference is using 10 psf wl making? extra nailing at the roof diaphragm or shear walls? additional shear walls required?
i have done a lot of one story wood structures, and usually "standard" construction (1/2" or 5/8" osb on the roof, 7/16" osb on the walls, nails spaced at 6/12) is sufficient.
daveatkins
dave, the one story projects we do oftentimes are 2 and 3 times longer than they are wide, and they're 16' tall and taller. the lateral load that is applied to the heel of my trusses, for post / diaphragm interaction analysis, can double when using the 10psf on the vertical projection compared with calculating the pressures in each zone.
most often these are steel-clad wood diaphragms. we're talking lots of stitch fasteners and supplemental chord force fasteners to keep the building from ripping apart!
that is why this is such a big deal. also, there is the need for a lot more shearwalls on the end bays or the need for intermediate shearwalls, if possible.
thanks.
i see--you are doing a post frame building. i feel your pain--i know that you get large chord forces which necessitate a lot of nails or even lag screws in the purlin to purlin connections. do you have the post frame building design manual? it has a method for distributing the chord force among all the purlins, not just the edge purlins.
daveatkins
__________________
借用达朗贝尔的名言:前进吧,你会得到信心!
[url="http://www.dimcax.com"]几何尺寸与公差标准[/url]
huangyhg离线中   回复时引用此帖
GDT自动化论坛(仅游客可见)
 


主题工具 搜索本主题
搜索本主题:

高级搜索
显示模式

发帖规则
不可以发表新主题
不可以回复主题
不可以上传附件
不可以编辑您的帖子

vB 代码开启
[IMG]代码开启
HTML代码关闭

相似的主题
主题 主题发起者 论坛 回复 最后发表
100 or 100 = 25 huangyhg 产品功能分析 0 2009-09-06 10:27 PM
load comb and 1.0 factor of safety huangyhg 产品功能分析 0 2009-09-06 10:23 PM
ad load factor in asd huangyhg 产品功能分析 0 2009-09-06 10:22 PM
fastener load distribution huangyhg 精密机械 0 2009-09-05 10:44 PM
【转帖】missing entities in load, but old toolkit did load all yang686526 DirectDWG 0 2009-05-06 05:52 PM


所有的时间均为北京时间。 现在的时间是 11:07 PM.


于2004年创办,几何尺寸与公差论坛"致力于产品几何量公差标准GD&T | GPS研究/CAD设计/CAM加工/CMM测量"。免责声明:论坛严禁发布色情反动言论及有关违反国家法律法规内容!情节严重者提供其IP,并配合相关部门进行严厉查处,若內容有涉及侵权,请立即联系我们QQ:44671734。注:此论坛须管理员验证方可发帖。
沪ICP备06057009号-2
更多