默认 another concrete corbel question

another concrete corbel question
hi everyone,
an existing corbel is to support a new precast beam. the corbel doesn't have the capacity to resist the reaction from the beam. can we provide plates like the ones shown in the attached sketch welded to existing embedded plates in the column to reduce the load applied on the corbel? we thought we can do load distribution between the corbel and the new plates based on relative stiffness. how?
1- apply a unit load on the corbel and the plate and calculate deflections due to bending, compression, and shear,
2- the load carried by the corbel/the load by plate = deflection in plate/deflection in corbel.
is this correct?
if yes, what do you think can go wrong? btw, we know that carrying all the load on the corbel is more certain approach, but the corbel, that is one of many, need be demolished and re-built, which we don't mind doing if other ways are not available.
compatibility of deflections and distribution of load is not the way to go with this problem. either the web connection or the corbel will fail first, then all the load goes on to the other element.
i agree with hokie.
the corbel is infinitely stiffer than the angles you show an will fail before any significant load gets taken by the angles (it already is taking all the existing load).
how are the existing corbels failing?
csd72,
the corbels are not failing. they are built now. the beams are not istalled yet but they have higher loads now than what the corbels were designed for.
enlarge the cornel by make it deeper if you could.
watch for rotation restraint due to the plates and moment into the column.
kslee1000,
we were hoping the plates can do it because this is much faster way. in our relative stiffness analysis, we assumed a cracked concrete section and full fixity for the plates, which is why we have uncertainty in this solution. the result of this analysis showed about 65% load to be carried by the corbel and 35% by the two plates, which would be adequate.
haynewp,
we were to carry only vertical shear on the new plates. we're allowing for horizontal movements by providing slotted connections.
any ideas are welcomed.

your detail creates a end point with partial moment restrain, which is not easy to evaluate. if you have confidence in the proportion of load sharing, then, yes, it is a much friendly solution. however, be prudent, watch out on effects on the precast beam end, column, and the plates.
one positive thing is your detail tends to diminish the lateral load on the corbel. good luck.
ailmar, i'd still say hokie has a good point. there is, in reality, a high difference in stiffness between the side plates and the corbel. since the corbel is so much stiffer than the plates, it will initially take most of the vertical load.
if "most of the vertical load" is more than what the corbel can safely support, it may then experience damage, distress or failure. this distress would mean the corbel, to some extent, moves or shifts such that the load is quickly transferred to the plates, which cannot take the vertical load all that well based on your sketch.
it all doesn't look like a good solution to me.
a better solution would be to strengthen the corbel directly. possibly by constructing a support corbel beneath it.

plates on both sides of the column/corbel with through bolts can be designed for the entire reaction of the beam. grout any voids to bring the sides into plane.
add'l precaution:
the precast beam, when loaded, tends to rotate upward. the rotation is restrained by the plates with a couple in them. watch out for the extra pulling/pushing forces - are both the column and the precast beam are capable to resist the forces without doubt.
__________________
借用达朗贝尔的名言:前进吧,你会得到信心!
[url="http://www.dimcax.com"]几何尺寸与公差标准[/url]
huangyhg离线中   回复时引用此帖
GDT自动化论坛(仅游客可见)
 


主题工具 搜索本主题
搜索本主题:

高级搜索
显示模式

发帖规则
不可以发表新主题
不可以回复主题
不可以上传附件
不可以编辑您的帖子

vB 代码开启
[IMG]代码开启
HTML代码关闭

相似的主题
主题 主题发起者 论坛 回复 最后发表
angle bearing on concrete - prying force huangyhg 产品功能分析 0 2009-09-07 12:08 PM
anchor for concrete footing huangyhg 产品功能分析 0 2009-09-07 11:56 AM
30mpa parking garage concrete slab vs. 35mpa huangyhg 产品功能分析 0 2009-09-07 08:39 AM
3000 psi concrete requiremen huangyhg 产品功能分析 0 2009-09-07 08:39 AM
28 day vs. 56 day concrete breaks huangyhg 产品功能分析 0 2009-09-07 08:34 AM


所有的时间均为北京时间。 现在的时间是 12:46 AM.


于2004年创办,几何尺寸与公差论坛"致力于产品几何量公差标准GD&T | GPS研究/CAD设计/CAM加工/CMM测量"。免责声明:论坛严禁发布色情反动言论及有关违反国家法律法规内容!情节严重者提供其IP,并配合相关部门进行严厉查处,若內容有涉及侵权,请立即联系我们QQ:44671734。注:此论坛须管理员验证方可发帖。
沪ICP备06057009号-2
更多