默认 effects of wind loading on 40x20 banner

effects of wind loading on 40'x20' banner
i am working on the wall anchors for a large 40'w x 20'h banner which is to be suspended from the uppermost wall of an 11 storey building. the wall consist of 4 inch thick precast panels. i am trying to use 5/8" dia. through bolts spaced at 5'-0" on centre (top and bottom of banner).
as i apply my wind loading to the banner, i notice that i should be considering the effect of the resulting tension in the banner which in turn creates large shear loads in the bolts if the banner is tight to the wall (i.e. like pulling on the centre of a tight steel wire between two roof anchors. when there is very little slack in the wire, the resulting loading on the anchors perpendicluar to the applied load are large).
am i getting to analytical in considering this. should i just be considering straight pull out resulting from the wind on the specific anchor bolt's tributary area?
thanks
gmf
find a job or post a job opening
if your banner can't span to the bolts in bending, i think you need to consider the shear force due to the tension in the banner. limit the tension, though, to the strength of the banner. maybe even, the strength of the banner at the connection.
that is a real problem - the outside cables - if too tight will definitely fail the bolts in shear or the brick or whatever.
if you can keep the cable from sagging and do not preload too high - loads will not be too bad - in other words - more connections
basic equation:
h = wl^2/8d
h = tension
w = plf on cable
l = span
d = sag
watch units and good luck
gmf,
the catenary tensions forces will be the primary load on your anchors in this type of structure. i would expect the shear from this to be roughly 3 or four times the tension.
this is something that i have seen overlooked by many engineers and it is a good thing that you have picked it up.
look up the catenary formulii in roarks for the typical formulii for a one way cable. you can get a rough estimate of the average loads on each side by equating the deflection at the banner center.
the hardest thing on this will be determining the ea as this information is not usually readily available. i would suggest seeing if you can obtain elongation data from the manufacturer from which you can estimate the ea at the service loads.
keep in mind that inward pressure will blow the banner into the face of the building and therefore does not normally need to be considered.
the banner also will need to be tensioned to take the kinks out, they never get the size right. have you allowed for future banner replacement?
thanks everyone for the help. this has been great. i have been able to get a udl load confidently at the top and bottom of the banner using roark's and analyzing the banner as a simple flexible (cable) beam. now using the udl's i have obtained at the top and bottom of the banner, i am wondering if i have the same "flexible beam" effect within the banner perimeter edge (top edge for example) spanning between grommet holes, creating tension in the perimeter of the banner. i figure the tensions created in this case would cancel each other out based on adjacent spans, except at the corners of the banner where there is no adjacent span. would this be a correct way at looking at this? currently, i am connecting the banner grommet holes directly to the anchors above (spaced now at 2'-6") though i am wondering if i need an anchor level with the top of the banner with a horizontal tie
gmf,
as csd72 noted, the forces are catenary in nature. the only way to avoid shear forces on the anchors is to provide a compression frame against the wall to resist that component.
i would bring those anchors in closer and use an aluminum flat bar in a fabric sleeve rather than grommets (which are great starting points for tears).
i stress again that the fabric manufacturer will definately not get the banner size right and you should allow 3" tolerance to allow for this.
__________________
借用达朗贝尔的名言:前进吧,你会得到信心!
[url="http://www.dimcax.com"]几何尺寸与公差标准[/url]
huangyhg离线中   回复时引用此帖
GDT自动化论坛(仅游客可见)
 


主题工具 搜索本主题
搜索本主题:

高级搜索
显示模式

发帖规则
不可以发表新主题
不可以回复主题
不可以上传附件
不可以编辑您的帖子

vB 代码开启
[IMG]代码开启
HTML代码关闭

相似的主题
主题 主题发起者 论坛 回复 最后发表
effective wind area huangyhg 产品功能分析 0 2009-09-08 09:45 PM
british wind loading codes huangyhg 产品功能分析 0 2009-09-07 05:19 PM
balcony guardrail wind huangyhg 产品功能分析 0 2009-09-07 02:11 PM
asce figure 6-10 wind loads huangyhg 产品功能分析 0 2009-09-07 01:22 PM
asce 7 wind loading of perforated surfaces huangyhg 产品功能分析 0 2009-09-07 12:59 PM