默认 load combination questionpoll

load combination question/poll
a question for the structural engineering community: the asce/ibc load combinations include a combination under the asd basic load combinations for d+(w or e)+l+(lr or s or r). when two or more transient loads are combined in this section a 0.75 factor on the live loads may be used. now here is the question, how many engineers use this load combination for c&c design of say a rafter or bar joist?
here is an example that would be typical for my part of the country. assume a roof snow load of 20 psf (unreducible) and the wind load minimum inward pressure of 10 psf.
s = 20 psf
w = 10 psf
0.75(20 psf + 10 psf) = 22.5 psf > 20 psf for snow
however, i don't know personally of any engineers who would design for 22.5 psf in this case as nobody combines the roof live load with wind.
the typical interpretation i hear is that this load combination is intended for design of elements such as columns where axial load results from the lateral loads.
do you agree or disagree???
check out our whitepaper library.
technically you'd use the 22.5 psf. for a bar joist, the wind+snow would be checked (for the typical joist tables) as a live load.
on a bar joist roof, i don't think wind and snow would ever be additive--the wind would typically be uplift.
daveatkins
depends on the roof - there are wind combinations in asce 7 that require a downward wind pressure - primarily on windward slopes.
the multiple tranient live load reduction is used quite often in designing roof trusses. you can see the advantages especially when designing attic trusses. it make it quite difficult to properly load girder trusses with the common trusses taking advantage of the live load reduction. metal-plate connected roof trusses may also be designed using a hybrid method: the component is designed for c&c and the uplift reactions are mwfrs.
woodengineer
thanks for the comments. the asce wind loads have both positive and negative pressures that must be checked. i think many engineers tend to "forget" or "neglect" the positive pressures, but according to the required load combinations these should be combined with the roof live load (snow, live, etc.). does anyone other than jae actually use this load combination?
i believe the positive wind pressure on roofs is the minimum of 10 psf unless teh roof slope exceeds (or equals) 45 degrees. i would check it for positive wind pressure (not a positive value of the negative wind pressure).
structuraleit:
yes, that is what i meant. in the example i used in the orginal post, i combined the 10 psf positive wind pressure with the assumed 20 psf roof snow. thanks for clarifying that.
well, you learn something new every day. i see that there is a gcp coefficient for positive pressure on a flat roof. i did a quick example--under 15' eave height, exposure b, 90 mph wind, iw = 1.0, and found the positive pressure to be 5.92 psf.
here is where engineering judgment comes in--when combining wind load with live load, i think you could use 3/4 of the 5.92 psf plus 3/4 of the 20 psf, which is 19.4 psf. and so 20 psf live load would still control. i think wind acting alone with dead load would need to be the 10 psf minimum, but then that wouldn't control either.
i suppose if you have a higher eave height, exposure c, or iw > 1.0, live load plus wind load would control.
but--isn't the 20 psf an arbitrary minimum roof live load? if you are in a five psf snow load area, for example, could you combine 3/4 of the snow load based on five psf with 3/4 of the 5.92 psf wind load, and then compare that to 20 psf?
just some food for thought.
daveatkins
wouldn't the wind load used in the combination would still have to be 10 psf minimum? section 6.1.4.2 of asce7-05 states that a minimum design wind pressure for c&c shall not be less than 10 psf acting in either direction.
daveatkins is correct in that for areas of the country with small roof snow loads this particular load combination would not control. it would also not control for large snow loads as the 25% reduction would more than account for the (net) 7.5 psf wind.
i've always said that the day i stop learning will be the day i die.
i usually check the positive wind load along with live at the roof. in my area the positive wind load tends to be a bit larger than 10 psf so it becomes important. in the end the difference is not a lot, but it counts for being thorough. i don't agree that truss uplift reactions are necessarily mw, but that can be in another thread, and has been in several.
__________________
借用达朗贝尔的名言:前进吧,你会得到信心!
[url="http://www.dimcax.com"]几何尺寸与公差标准[/url]
huangyhg离线中   回复时引用此帖
GDT自动化论坛(仅游客可见)
 


主题工具 搜索本主题
搜索本主题:

高级搜索
显示模式

发帖规则
不可以发表新主题
不可以回复主题
不可以上传附件
不可以编辑您的帖子

vB 代码开启
[IMG]代码开启
HTML代码关闭

相似的主题
主题 主题发起者 论坛 回复 最后发表
gravity load distribution huangyhg 产品功能分析 0 2009-09-09 03:06 PM
effects of a load on sog and below grade huangyhg 产品功能分析 0 2009-09-08 09:45 PM
dissecting a load combination huangyhg 产品功能分析 0 2009-09-08 06:58 PM
asce 7-98 load combination huangyhg 产品功能分析 0 2009-09-07 01:19 PM
ad load factor in asd huangyhg 产品功能分析 0 2009-09-06 10:22 PM


所有的时间均为北京时间。 现在的时间是 06:08 AM.


于2004年创办,几何尺寸与公差论坛"致力于产品几何量公差标准GD&T | GPS研究/CAD设计/CAM加工/CMM测量"。免责声明:论坛严禁发布色情反动言论及有关违反国家法律法规内容!情节严重者提供其IP,并配合相关部门进行严厉查处,若內容有涉及侵权,请立即联系我们QQ:44671734。注:此论坛须管理员验证方可发帖。
沪ICP备06057009号-2
更多