load testing
we have completed an analysis of an existing pre-eng building built in 1975. the frames were overstressed by 150% under unbalanced loads. the purlins were overstressed by over 100% under normal snow load and finally the girts were overstressed by 100% under wind. once reported to the client, two separate engineering firms completed peer reviews, both agreeing with our conclusions.
the problem is the second firm recommended a load test. i have been asked to comment on their procedure. how is it possible to load test such a building without failing the structure or if local testing is done how you prevent adjacent frames from contributing to the resistance.
i have talked to other engineers who all agree that load testing does not seem reasonable. your comments would be appreciated.
onteng
i would be interested in what the cost difference between repairing and load testing the structure is.
i agree that a meaningful load test is unreasonable. being a pre-engineered building, i assume it is primarily constructed from steel. since the allowable bending stress was 66% of the nominal yield strength (per aisc manual of steel construction, sixth edition), then testing to the calculated stresses (2 x 66%, or more) should cause yielding (but not collapse). of course yielding would most likely make the building unusable.
your insight into the complications presented by have unloaded adjacent frames is true. that is one of the times when engineering judgment on the interpretation of test results in essential. the true precision of load test results is low, it makes slide rule accuracy (3 significant figures) look good.
the only way a load test would work on a thin-engineered metal building would be if the engineer somehow knew or suspected that there was excess strength in framework that would allow loading up to a desired "ultimate" level. for these types of buildings its almost given that they were or are designed to the nat's ass and as slideruleera states, it most likely would go past yielding.
your separate analyses also suggests that a load test would be fruitless.
the only reasonable approach to such a load test would be to do a load deflection curve up to, say, 75% of design and see how well the actual curve follows the predicted curve. even then, it is difficult to perform a load test on a pre-engineered (don't ya just love that term...pre-engineered...as if other buildings were not!)steel building.
at uni i compared predicted and actual load deflection curves for single welded trusses. off the top of my head the results were ok, within say 10%. but that is for a single,welded, truss with a point load and defined terminations.
thanks for all the replies.
if the problem with load sharing is eliminated, i still see problems. the webs are very thin with no web stiffeners and i am concerned that they buckle and cause collapse. i one frame collapses, it may pull the other frames down.
at this point i am not sure how they expect to load the frames and keep the techs safe during the test. i don't think i want to be in the building when they do this test.
we have had discussions with one engineering firm who indicated hundreds of thousands of dollars for testing. this does not include any costs for replacement frames once they yield. our budget for reinforcing is about $1.8m.
onteng....the cost estimate for the load test is probably in the right range. i've done load tests that exceeded $100k.
i have gone to remote monitoring of load tests for safety.
we used to set dial indicators and read each one as the load was applied, often being under the load with catch shoring (set catch shoring to a level below the expected deflection x 2).
since about 1992 or so, all load tests i've done have been done using remote sensing and strain gages/electronic dial indicators connected to laptop computers, where monitoring can be done outside the loaded area. loading can be done hydraulically, either pushing or pulling on the
are you friendly with the firm that suggested the load test? maybe it is time to discuss with them why they felt that would help. it could be that it is just something standard that they typically say to limit liability. although it would probably be pretty interesting to load test the structure, it sounds like a definite waste of money with
ron, thanks for the testing input. i will discuss this with the company overseeing the testing.
i had discussed this testing previously with the engineer from the firm who recommended it. at that point, he felt the load testing may not be practical. i think the final say may have been taken out of his hands.
i thank everyone for their contribution. my reservations to testing have been reinforced.
this project is a political issue and i just want to be out of the way when this thing blows up, so to speak.
a couple of comments:
load testing should mimic that various load conditions the building should be designed for.
hydraulic load cells work well because the load falls of quickly on pending failure.
digital 'dial gauges' as ron noted with laptops; i've used both these and lvdt's for distance measuring.
pre eng buildings are generally designed elastically but are contoured such that yielding (and plastic collapse) can occur at many points almost simultaneously.
you might want to look at "shakedown pheonmena' for plastic structures. it's possible for parts of the structure to yield and that under a different loading, the residual stresses causing a collapse load at a smaller load than anticipated.
dik
__________________
借用达朗贝尔的名言:前进吧,你会得到信心!
[url="http://www.dimcax.com"]几何尺寸与公差标准[/url]
huangyhg离线中   回复时引用此帖
GDT自动化论坛(仅游客可见)
 


主题工具 搜索本主题
搜索本主题:

高级搜索
显示模式

发帖规则
不可以发表新主题
不可以回复主题
不可以上传附件
不可以编辑您的帖子

vB 代码开启
[IMG]代码开启
HTML代码关闭

相似的主题
主题 主题发起者 论坛 回复 最后发表
load testing wood structure huangyhg 产品功能分析 0 2009-09-10 11:14 AM
load testing of concrete structures huangyhg 产品功能分析 0 2009-09-10 11:13 AM
load combination questionpoll huangyhg 产品功能分析 0 2009-09-10 11:01 AM
effects of a load on sog and below grade huangyhg 产品功能分析 0 2009-09-08 09:45 PM
drilled piers and load testing huangyhg 产品功能分析 0 2009-09-08 07:46 PM


所有的时间均为北京时间。 现在的时间是 07:35 AM.


于2004年创办,几何尺寸与公差论坛"致力于产品几何量公差标准GD&T | GPS研究/CAD设计/CAM加工/CMM测量"。免责声明:论坛严禁发布色情反动言论及有关违反国家法律法规内容!情节严重者提供其IP,并配合相关部门进行严厉查处,若內容有涉及侵权,请立即联系我们QQ:44671734。注:此论坛须管理员验证方可发帖。
沪ICP备06057009号-2
更多