does anyone know the formula for lu, please? lu is the maximum unbraced length of compression flange at which the allowable bending stress may be taken as 0.60 fy.
my civil engineering reference manual, 8th ed. on page 59-3 provides lu as the larger of 20000*cb/((d/af)fy) or rt*(102000*cb/fy)^1/2. however, i think there is a typo in the first equation as i can't seem to get the right lu.
for instance, with a w14x120 shape, aisc manual 9th edition provides an lu of 44.1 feet. i am not able to replicate it with the formulas from cerm. i am using a cb value of 1.0.
hope someone can help. please provide references, too, in aisc or online, if possible, so i can look them up myself. thanks a bunch.
lu is the unbraced length of your steel
thanks for the prompt response, 3doorsdwn. no, i am looking for the formula for lu, which is the maximum unbraced length of compression flange for which fb=0.60fy.
lc is the maximum lengthn of compression flange for which fb=0.66fy.
does anyone know of an accurate formula for lu, please? i found a reference to it in my cerm 8th ed, but can't seem to get the same lu as published in aisc manual, 9th ed. appreciate any help.
you may be`a victim of a typo.
lc is the braced length at which a compact section can have an allowable stress of .67 fy in asd.
lc = the smaller of (76bf)/(sqrt fy) or 20,000/((d/af)fy)
lu is the unbraced length where the allowable stress is less than .6 fy.
this is governed by 3 equations,of which the
sqrt (102000*cb/fy) listed above is one.
best bet is to get a copy of the green aisc book.
in asd, when lb exceeds lc, then fb <= 0.66fy. the formulas for such case are a function "l" and "rt". you could set fb = 0.6fy and solve each condition of l/rt for what you refer to as "lu".
both equations look correct to me. cb must be 1.0. these are from equations f1-6 & f1-8 from the 1989 asd "green book".
fb = {2/3 - (fy(l/rt)^2 / 1,530,000cb)} x fy
fb = 12 x 10^3cb / (l x d/af)
in each case l must be solved for and then equals lu.
mrfurleyeit:
check aisc 9th edition, pg. 2-30. bagman2524 and roadtech are right on the money!
thank you so much for your responses, people; roadtech, bagman2524, et. al. and esp. jike for giving the reference in the "green book" as page 2-30. the formulas on that page for lu are exactly the same ones that i put in my original question, i.e. lu as the larger of 20000*cb/((d/af)fy) or rt*(102000*cb/fy)^1/2. i got mine from the civil enginereing reference manul, 8th ed. though.
here's my thing, though. i think i can illustrate better with a wide flange section, say w14x120. for this column shape, the lu is 44.1 feet (page 3-23). rt=4.04, d=14.48, a=35.3. i am using a36 steel. i am using a cb value of 1.0.
plugging these variables into the two formulas for lu, i get:
(i) 20000/[12(14.48/35.3)36] = 112.86, or
(ii) [sqrt(102000/36)]*(4.04/12) = 17.92
since lu is the larger or either (i) or (ii), i am getting an lu value of 112.86 feet.
the lu value given in aisc, 8th ed for w14x120 is 44.1 feet. what gives? i must be doing something wrong. am i doing something wrong?
how do i get an lu of 44.1 feet from the formulas for lu. thanks in advance, and sorry, i may get some egg on my face, but i hope to find a resolution for this. please provide your calculation, also.
you should be using d/af, not d/a. af is the area of the flange. for w14 x 120, d/af = 1.05 (from green book).
20000/(12 x 1.05 x 36) = 44.1 ft.
d/af is given in the book but you could also calculate it yourself.
af = tf x bf = 14.670 x 0.940 = 13.79
d = 14.48
d/af = 14.48 / 13.79 = 1.05
thanks for helping out, people. the discussion and feedback was very useful and i hope, useful, to others, as well. my oversight, as i see it, is to use a, instead of af, in my calcs. the other parts of the formulas were ok, but discussing and going to and fro about it reinforces the understand of this particular subject, which i think is very useful for the long term.
now, if you'll excuse, i've got some egg i need to wipe off my face
__________________
借用达朗贝尔的名言:前进吧,你会得到信心!
[url="http://www.dimcax.com"]几何尺寸与公差标准[/url]
huangyhg离线中   回复时引用此帖
GDT自动化论坛(仅游客可见)
 


主题工具 搜索本主题
搜索本主题:

高级搜索
显示模式

发帖规则
不可以发表新主题
不可以回复主题
不可以上传附件
不可以编辑您的帖子

vB 代码开启
[IMG]代码开启
HTML代码关闭

相似的主题
主题 主题发起者 论坛 回复 最后发表
difference between transfer length develop. length in pres huangyhg 产品功能分析 0 2009-09-08 06:43 PM
cantilevered beam backspan- unbraced beam length huangyhg 产品功能分析 0 2009-09-07 10:42 PM
calculation of guy wire length for tall guyed mas huangyhg 产品功能分析 0 2009-09-07 10:07 PM


所有的时间均为北京时间。 现在的时间是 11:03 AM.


于2004年创办,几何尺寸与公差论坛"致力于产品几何量公差标准GD&T | GPS研究/CAD设计/CAM加工/CMM测量"。免责声明:论坛严禁发布色情反动言论及有关违反国家法律法规内容!情节严重者提供其IP,并配合相关部门进行严厉查处,若內容有涉及侵权,请立即联系我们QQ:44671734。注:此论坛须管理员验证方可发帖。
沪ICP备06057009号-2
更多